Nicholas

Hello,
I don't usually do domestic work but have a friend who needs work done.
he said an electrician he had out a few months ago said the distance from the red like and meter was to far away from the consumer unit. Is there a regulation covering this?

thanks!
 
Yea the solid link that feeds the meter. Sorry for the confusion thought everyone called them red links.

not sure if he means the length of tail from meter to unit. Or just the general distance between the two.
they are only a couple meters away from each other. The meter and red link is in the front porch and consumer unit in the hall way. The distance the tail travel is about 10meters. Up into floor space and back down to consumer unit.
 
Right i might be getting confused to be honest. I havnt looked at this yet and only going by what I've been told.
its probably a fuse feeding meter then consumer unit.
 
This is a house. I'm used to doing flats fed from ryefield units. Which feed what we call the red links.
 
I've worded this so bad lol
so is there a maximum distance between the fuse/meter/consumer unit?
 
If the service head and meter are more than 3 metres away from the CU then a switch fuse should be installed after the meter
Something like that anyway, I'm knackered and have a blinding headache so can't be bothered to go and get the proper info.
Sorry mate.
 
Oh I get you now. I keep typing to slow lol. Ignore my little messages.
thanks for your help guys. His is definitely longer than 3 meters.

thanks guys. Sorry for the bad explanation!
 
If the service head and meter are more than 3 metres away from the CU then a switch fuse should be installed after the meter
Something like that anyway, I'm knackered and have a blinding headache so can't be bothered to go and get the proper info.
Sorry mate.

What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.
 
What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.
What? Really!?
 
The length actually varies between the different DNOs, on a recent meter move by ukpn the paperwork clearly states a maximum of 4metres.
 
What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.

The point is that the DNO specify a maximum length of tails which are allowed before the consumer must provide their own protective device. Generally this is 3 metres but some allow 4 and others 2.5
 
What's the point in that? If the cut out has a 100A fuse why then put two in sequence? Can't see the need. I only bother using a kmf if the mains is ran in 16 te and dumb it to 80A. Plus the dno supply a dual pole isolator.

Do you do this for flat sub mains then? Can't see how the DNO would accept this.
 
Do you do this for flat sub mains then? Can't see how the DNO would accept this.

Yes when we do the meter cupboards for flats we go from our kmf to the dual pole isolator supplied by the dno. But for houses we never use this setup. We just go from consumer to dual pole isolator. I never knew to be fair, but I still can't see the need for it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Distance from red link to consumer unit
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
Nicholas,
Last reply from
LankyWill,
Replies
31
Views
10,378

Advert

Back
Top