I’ve found a couple of installations (TNCS) where the location of the MET is not clear.
In both cases, gas/water bonding has been run back to either/or the DNO break-out “MET” or to the Consumer Unit. "There can only be one MET"
The first one I sorted out and created just one MET.
The new one, I find gas bonding to service head break-out location, and water bonding to CU. In this case it will be hard to extend water bond back to the service head break-out located MET, or the gas bond up to CU - which would make the CU the MET.
This is effectively making the 16mm Earthing Conductor a combined earthing Conductor and bonding for the water, - but not for the gas.
So I am thinking that if a “open supply neutral” current happened to pass up water pipe, it could create a voltage down the length of the earthing conductor, which would then put gas bond at a different potential to water bond.
So “There is only one MET”..Of course. But can I /should I leave this one since it’s tricky to get right? - Or attempt to get (say) water bonding back to break-out MET (albeit would need a crimped joint in the bond, and make a mess of the Décor).
In both cases, gas/water bonding has been run back to either/or the DNO break-out “MET” or to the Consumer Unit. "There can only be one MET"
The first one I sorted out and created just one MET.
The new one, I find gas bonding to service head break-out location, and water bonding to CU. In this case it will be hard to extend water bond back to the service head break-out located MET, or the gas bond up to CU - which would make the CU the MET.
This is effectively making the 16mm Earthing Conductor a combined earthing Conductor and bonding for the water, - but not for the gas.
So I am thinking that if a “open supply neutral” current happened to pass up water pipe, it could create a voltage down the length of the earthing conductor, which would then put gas bond at a different potential to water bond.
So “There is only one MET”..Of course. But can I /should I leave this one since it’s tricky to get right? - Or attempt to get (say) water bonding back to break-out MET (albeit would need a crimped joint in the bond, and make a mess of the Décor).