Hi thanks for the replies, apologies for resurrecting an old post i was just having a browse through.
Yeah i agree with the point about hiding faults with RCD's
I was trying to work out the theory side of things, even though the Ze is above the allowed maximum, it is still going to be lower than a TT Ze so just wondered why it was the norm to TT installations that exceed the maximum Ze values on TNS and TNC-S systems.
Cheers
The real bottom line to this is stability. Your quite correct the chances of you finding a TT system of less than 5 ohms is slim to virtually unheard of, but the protection system for a TT is designed slightly differently, well it was in the past.
Before the 17th there was only very certain exceptions for additional protection by RCD, one that instantly springs to mind in the 16th was a socket outlet for use of equipment outdoors, another was TT systems.
For as long as I can remember TT systems have utilized extra protection in either the old ELCB or the modern day RCD. All TN systems didn't until the 16th and the out side socket
The reason for this is the low EFLI path that a TN system gave you, and the stability of the DNO earth. The ESQCR empowered the DTi to make the DNO to supply stable earthing for consumers, and though the ranges are not actually in the guide, it was decided that a TN-S should be 0.80 and TNC-S 0.35.
If you found an installation that exceeded these values it would be an indication of a fault and as Tony said you really should not be masking a fault.
Yes an RCD would work in this instance, but you are not clearing the problem, which if ignored could mean a situation where the fault escalated to either a blown cable or leaving an installation without an earth at all. This is why we test.
I'm sure as you carry on working you will find a TN-S system that has an upfront RCD/ELCB and wonder what the.....................often what happened in TN-S times there would be fault/maintenance on a joint and the old Electricity board would fit an upfront RCD/ELCB as a temporary fix, and it would be just left.