Hi, I have never come across this before but is it OK to put a DB on the ceiling. We have had some cabins in and the db's are all on the ceiling. I have said this is wrong but my supervisor insists it is OK. Any input would be appreciated.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Distribution boards location in the UK Electrical Forum area at ElectriciansForums.net
i agree with you, ref: post 10
just wondered if you could help me back it up with something easy to quote!
Which regulations don't apply to commercial buildingsRegulations do not apply to commercial buildings, Document M may not apply either otherwise it would be 1.2metres high max.
Quote from Consumer Unit regulations 2022Which regulations don't apply to commercial buildings
I agree just goes to show don’t believe all that you read , it is all down to interpretation & do you want to sleep at night.There are some regs that only apply to certain types of building, non combustible consumer units is of course one of them.
but to say regulations do not apply to Comercial buildings is simply wrong,
some Comercial buildings have far more regulations that apply to them than domestic.
Consumer units installed in domestic premises have to be non combustable there is no absolute requirement that they MUST be metal and the reg you quote says exactly that and only uses metal as an exampleQuote from Consumer Unit regulations 2022
The particular consumer unit regulation relating to this in the 18th edition is 421.1.201
It should be noted that this regulation does not apply to commercial installations, where plastic consumer units can still be installed.
Not only that, but in domestic outbuildings, for example sheds & garages, you can still install plastic consumer units assuming that the outbuilding is not joined to the main building.
Agreed . 421.1.201. Ferrous metal is deemed to be one example of a non-combustible material that meets the intent of the regulation.Consumer units installed in domestic premises have to be non combustable there is no absolute requirement that they MUST be metal and the reg you quote says exactly that and only uses metal as an example
Might want to have a read of the Approved Document M:Regulations do not apply to commercial buildings, Document M may not apply either otherwise it would be 1.2metres high max.
the electric will all fall out.i agree with you, ref: post 10
just wondered if you could help me back it up with something easy to quote!
Reply to Distribution boards location in the UK Electrical Forum area at ElectriciansForums.net