Hi all, I want to feed a small 2-way distribution board from a spare way in the main consumer unit.
The new 2-way board will have either two B6 MCBs for separate lighting circuits, or there'll be one lighting circuit and a separate socket circuit. What sized breaker do I need to use in the spare way in the main consumer unit and what csa for the feed cable from the main consumer unit to the 2-way board. The 2-way board has a 63 Amp double pole main switch. Thanks!
 
If you are enquiring as to what rating of device will provide Selectivity (discrimination), the simple answer is no two BS EN 60898 circuit breakers will discriminate with each other under fault conditions.
 
Hi all, I want to feed a small 2-way distribution board from a spare way in the main consumer unit.
The new 2-way board will have either two B6 MCBs for separate lighting circuits, or there'll be one lighting circuit and a separate socket circuit. What sized breaker do I need to use in the spare way in the main consumer unit and what csa for the feed cable from the main consumer unit to the 2-way board. The 2-way board has a 63 Amp double pole main switch. Thanks!

Where is the new DB going to be sited? How far away?

Whats the Ib?


You need to provide more info to be honest. This is pretty standard stuff. :)
 
Good job I checked your profile mate I was about to go into print with some abuse, but you're a Trainee so all is forgiven, just take note of the advice already given it's sound advice from knowledgeable people.
 

Reply to Distribution Circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
688
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
652

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
699
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
600

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top