I am a Yank electrician, I cant find where in 16th or 17th edition you have the
diversity factor for calculating loads.
Example:
1. In one office or sleeping room I put 4 power sockets on a 32 amp ring circuit.
We have 100 identical sleeping rooms or offices. What is the total load
that we calculate to figure out feeder size to the panel?
This is just an example, Im looking for where in BS7671 to find the answer?:confused:
Example:
Unfortunately, the OSG and BS7671 will not be that much help in deciding the maximum demand in a real life situation.
100*32 = 3200A = complete nonsense!
or 32 + (99*16) = As above
You will need to look at the average demand for the whole lot or in groups.
PCs, lighting, telecomms et al
If there are no electric heating appliances then the overheads will drop considerably
CIBSE publish utilization tables relating expected electrical utilization with size of unit
Ackbarthestar -
You said "CIBSE publish utilization tables relating expected electrical utilization with size of unit "
do you have a link to that?
But check out the attachment from Article 220 from NEC 2008.
See how easy it is to calculate Demand Factor in the states!!!
  • NEC-art.220.demandfactor.pdf
Ackbarthestar -
That particular article doesn't appear to be that helpful, no wonder you are looking for advice.
Try this article : http://www.liv.ac.uk/safety/safety_issues/electricity1/electricity_in_buildings_cibse_code_K.pdf
not bang up to date but will give you an idea of British Building services electrical design
Reply to Diversity factor for calculating loads ??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...