jonboy1
Hi all, I have a question relating to diversity allowance for air conditioning units (ACU). I have been asked to install 6 no. three phase supplies for acu's in a school.
These have starting 14A Running (max.) 29A each.
Using the on-site guide (an old copy) I have used option 2 as guidance (Heating and power). I calculated total demand at 121 amps with the diversity applied. Can somebody confirm this is correct or is there now an option for ACU's.
Many thanks
Jon
These have starting 14A Running (max.) 29A each.
Using the on-site guide (an old copy) I have used option 2 as guidance (Heating and power). I calculated total demand at 121 amps with the diversity applied. Can somebody confirm this is correct or is there now an option for ACU's.
Many thanks