I have a client who wants me to install more than your normal stuff in a new built garage but looking at his mains board in house he is already on his limits here's my findings and calculations please correct me if Iam wrong
existing mains board 6 x 6amp lighting = 36amp after diversity =23.76
40amp cooker circuit after diversity =19amps 3 x 32amp final circuits after diversity = 57.6amps
he wants in garage
20amp for 2x 2.5kw heaters 16amp for radial sockets 16 amp for some fancy energy saving water heater from zip to supply shower 6amp for lighting i have added these to the circuits in existing board for my calculations and came up with 125.12amps demand obviously with a 100amp cut out we are way over but iam for once hoping that i have got the calculations wrong can anyone help
thanks in advance
ANDREW
existing mains board 6 x 6amp lighting = 36amp after diversity =23.76
40amp cooker circuit after diversity =19amps 3 x 32amp final circuits after diversity = 57.6amps
he wants in garage
20amp for 2x 2.5kw heaters 16amp for radial sockets 16 amp for some fancy energy saving water heater from zip to supply shower 6amp for lighting i have added these to the circuits in existing board for my calculations and came up with 125.12amps demand obviously with a 100amp cut out we are way over but iam for once hoping that i have got the calculations wrong can anyone help