i need to wire in a 200a distribution board from a 400a board in an ind factory. Do i take diversity into account. The on-site guide says no but the Bs 7671 says yes but doesnt state if its for distribution boards or single circuits
 
Yes industrial diversity is quite a complex design problem. You really do need to take into account what kind of work and loads will be expected on the installation.

If there are a motors in the installation the OSG do give you some diversity values in table 1B. 100% for the largest and then 75% for the next and so on for the remaninder.

Then if you have a lot of fixed loads then there is virtually no diversity you can use. But remember there will be loads you can off set these with ring finals, offices, store areas etc etc.

I always use a rule of thumb for industrial of adding up the protection devices and times by 0.8. Add up each phases PD and do that and whatever is the largest phase load that is your man.
 
I thought you can only use diversity for seperate circuits i.e feeding 3 off cookers etc. At the bottom of the page of the osg in the diversity section under the table, it says diversity can not be used for a supply to a distribution board, the supply cable must take the total load
 

Reply to diversity of main supply for distribution board in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top