Hello all,
Have a potential 2 flat in the near future which are both tiny 1 bed flat. It consists of:
Cooker 3kw,hob 5kw,3 electric 1kw heaters,7kw shower,2kw under sink heater(not instantaneous) light and 2 rings. After diversity calcs i come to about 70 amps. I still think that this is a bit excessive as the chance of the shower being on with the cooker is limited and everything being used at once do to the fact at most there is going to be two people living there.
I was thinking of 80 amp switch-fuse supply the flat with 16-mm t/e with additional 10 mm g/y. clipped direct. the incoming is a three phase 100 amp supply. What are peoples thoughts on the max demand as i still feel that a 63 amp switch fuse would be more than adequate as most domestic properties i have come across are fine on 60/80 amp.
Add the protection devices up and *0.4 that is as near as most for a good way to do it or you could do it as in OSG pg 97 table 1B part 9 in the table.
T+E sub mains, unless you run it surface or try and put it through some earthed conduit, your going to have to RCD protect that with a 30mA one. Not feasible to run SWA?
Reply to Diversity in the Australia area at ElectriciansForums.net
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...