hi i have done a board change on a property for my assesment working out max demand with diversity is giving me a result of 152 amps due to there being 3 rings and 2 single sockets on seperate circuits really boosting the demand i know it will never pull this can someone suggest what to put in the maximum demand box and di i need to write anything in the comments box on the eic any help would be great thanks
 
ok
cooker on 40 amp 10kw cooker
kitch skts 32
garagge 32
conservatory skts 32
wc skt 16
total lights 25 fittings advergage 100 watts each
down sockets 32
up skts 32
loft skt 20
immersion 2.8 kw 16 amp
boiler 16amp

p.s lights are on 4 circuits all 6 amps
cutout fuse is 60 thanks
 
Add all the breakers up = 292x 0.4= 117A. and remember not all will be on at the same time that will never amount to that figure quick enough to blow the fuse, check the time curve tables for a BS1361 Type II fuse in the regs and that'll take over a 1000 seconds to blow im guessing. By which time things would be started to switch off.

Your going to get alot of different answers on this one from different Sparky views, but personally I'd change that fuse to a 100A to be safe.
 
No you can't as it's sealed and not your property. You will have to contact the DNO to upgrade.
What I would do is show your workings and your reasonings. Before the assessment if possible contact DNO, maybe they will give u a date to come and upgrade. Than at least you've got something to show them.
Good luck and let us know.
 

Reply to diversity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Gents has anyone done an application using the UKPN smart connect portal for a split phase supply and addition of multiple single phase battery...
Replies
0
Views
401

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top