anyone know what the likely breaking capacity and fuse type is for the 250A bs88's the elecy board fit on a commercial supply intake ?
cant check myself on the job i'm at without removing the cut-out chamber cover that has danger of death stickers all over it lol
even i'm not reckless enough to cut the ( very new ) seals on that bad boy :)
 
anyone know what the likely breaking capacity and fuse type is for the 250A bs88's the elecy board fit on a commercial supply intake ?
cant check myself on the job i'm at without removing the cut-out chamber cover that has danger of death stickers all over it lol
even i'm not reckless enough to cut the ( very new ) seals on that bad boy :)

Most BS88 fuses of that sort of size will generally be 80KA.
 

Reply to DNO fuses in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top