We've received a note from WPD with an application which has been approved in South Wales which is out of our usual area although same DNO different office:
''As a temporary measure(until 2nd March 2012) G83/1-1 may be applied to inverter connected generators rated between 16A per phase and 17kw per phase (ie 17kw for a single phase device,34 kw for a split phase device and 50 kw for a 3 phase device) as long as all of the following criteria are satisfied:
The third point is the one I'm concerned about ,having looked at the G83/G59 certs for SMA inverters which we use the most the over frequency setting is
G83 50.5 Hz +/-0.5 % at <5 seconds
G59 limit 51.5Hz <90s 52Hz <0.5s
These new figures are between the two
Can I change this using Sunny Explorer (with Grid guard code)? I have to admit I've not had to make any changes to the settings (other than the passwords) before although I'm sure I've seen it on the adjustable parameters
any advice would be appreciated
As for confirming the new setting is this a case of just adding a note to the commissioning form stating that its been changed or is a printout likely to be required?
And out of curiosity anyone know why they would do this as a temporary measure ,will this mean that they may revert to original settings at a later date ,and will we have to alter already installed systems later on?
I have sent these questions to the DNO and await their reply
''As a temporary measure(until 2nd March 2012) G83/1-1 may be applied to inverter connected generators rated between 16A per phase and 17kw per phase (ie 17kw for a single phase device,34 kw for a split phase device and 50 kw for a 3 phase device) as long as all of the following criteria are satisfied:
- The G83/1-1 stage 2 process is followed
- The Generator is connected through an inverter that is type tested to G83/1-1
- The over frequency protection setting is set at 51.5Hz with a time delay of no more than 0.5s . Note a setting below or above 51.5 Hz is not acceptable. All other protection settings shall comply with the Requirements G83/1-1
The third point is the one I'm concerned about ,having looked at the G83/G59 certs for SMA inverters which we use the most the over frequency setting is
G83 50.5 Hz +/-0.5 % at <5 seconds
G59 limit 51.5Hz <90s 52Hz <0.5s
These new figures are between the two
Can I change this using Sunny Explorer (with Grid guard code)? I have to admit I've not had to make any changes to the settings (other than the passwords) before although I'm sure I've seen it on the adjustable parameters
any advice would be appreciated
As for confirming the new setting is this a case of just adding a note to the commissioning form stating that its been changed or is a printout likely to be required?
And out of curiosity anyone know why they would do this as a temporary measure ,will this mean that they may revert to original settings at a later date ,and will we have to alter already installed systems later on?
I have sent these questions to the DNO and await their reply