Thats alright, until you come to do a CU change on the top floor flat.

Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
 
Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
Not necessarily, some establishments are not so simple. I recall from some of the comments placed on the draft, asked this conundrum and allegedly why the committee put the reg change on hold for the time being.
 
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
 
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
It will be a similar requirement to that of EV installations where an additional electrode connected to the PME arrangement, during an open pen circuit the touch voltage from exposed parts to true earth must not rise above 70v (hand to foot for EV but may require to be 50v hand to hand contact between exposed parts)
This in reality is hard to achieve as per examples in section 722 annex and guidance note 5 and 7 examples.
[automerge]1574883321[/automerge]
Being on the top floor, or any other floor, is irrelevant. The PME earth terminal and MET will still be at ground or basement level wherever the DNO cutout is.
That’s a sweeping statement considering there are many set ups where flats have their own DNO supplies complete with metering and are situated on many floors, be it older type accommodation/schemes.
 
Last edited:
Excuse my ignorance, but how does installing an earth electrode in addition to a PME earth mitigate the effects of an open PEN conductor? Is it something to do with a gradual voltage drop between that electrode and the 1st (or all?) earth stake of the PEN?
As I understand it, say the PEN breaks in the road, the current from let’s say house 1 (brown phase) They are using 50 amps, it a family of 4 at dinner time. That current is still going to try and flow back to the transformer but can’t, so it will find the shortest path, which will happen to be up the neutral of house 2 (black phase) House two may only be a little old lady and she only has a lamp and her Tv on so say she is using 5 amps. What is start to happen is she is going to get 400v turning up at her, appliances. And things starting to go bang, it will add a picture of this as well. So if there was an earth electrode at each house, it might help dump some of that stray current to earth, and trip some protective devices.
 
It will be a similar requirement to that of EV installations where an additional electrode connected to the PME arrangement, during an open pen circuit the touch voltage from exposed parts to true earth must not rise above 70v (hand to foot for EV but may require to be 50v hand to hand contact between exposed parts)
This in reality is hard to achieve as per examples in section 722 annex and guidance note 5 and 7 examples.

Thanks Ian, I'll have to take a closer look at that at the weekend with a fresh mind, there's no way I'll get my head around it now!
 

Reply to the thread, titled "DNOs forbid PME earth being exported???" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
DNOs forbid PME earth being exported???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
38

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Pretty Mouth,
Replies
38
Views
12,589

Advert

Back
Top