Need to get a feed in ready for an aircon unit, which will be on its own circuit. I'd usually put a rotary isolator in ready, but as the aircon guys will be there when I'm working it there a problem with taking the lead off the unit and putting it straight into the RCBO, with that used as the isolator if needed? The CU is only 2 foot away from where the aircon unit will be so sticking another point of isolation directly next to the CU seems a bit pointless!

Cheers :)
 
No not really as long as you don't need double pole isolation for instance if the system is a TT.
 
I see your dilemma with the cu only 2 foot away and that we can use the mcb/rcbo as a functional or isolation switch. I would put a rotary isso in just to make the install idiot proof for the users. Big red switch next to the aircon is better than finding a switch in a large board imho.
 
Agree with Malcolm

Although Paul has a point but evolution states that if you make something idiot proof, nature just evolves a better idiot :D
 
Last edited:
Thanks for perfectly demonstrating my dilemma :D Nice to see none of you can agree either! The rotary isolator would need to go outside so I might just see if I can get an outdoor one at the ready and then see on the day.

The system is TT, but as it can be isolated from the DP main switch on the 5 way unit we're installing the isolator for this piece of equipment (or any other for that matter) can be single pole can't it?
 
You can if you wish utilise the main DP switch as your means of isolation for that unit, but you would have to use that switch and not the single pole MCB all the time for isolation, which would means you isolate those other 5 circuits every time you want to isolate your unit, not a good design point really is it.

As it is TT use a double pole switch you could fit a double pole 20amp grid switch, won't need to be lockable if it's close by, or for extra safety a key type one.
 
remember that an MCB / RCBO is an 'off load' device and not designed for full load switching, I would put in an isolator as a mater of principle, if only for local isolation for the untrained. mechanical switching.
 
Thanks guys, I've ordered the usual crabtree rotary so will put that outside next to the unit and let the aircon guys take it from there. It seemed like a bit of a waste but better safe than sorry, especially as it's a TT.

Cheers :)
 
iv has same argument with a gaffer years ago He didnt want to fit isolator near db I argued that Onload and double pole He was stuffed when he checked the scope of works it said Every air conditioning unit shall have point of isolation next to it even indooor units fed from outdoor so the AC guys couldnt make mistakes turning off stuff
BIG RED BUTTON all the way
 
remember that an MCB / RCBO is an 'off load' device and not designed for full load switching, I would put in an isolator as a mater of principle, if only for local isolation for the untrained. mechanical switching.

Most likely the rotary switch that will be fitted would be to BS 60947-3 which is also a non switchable device on laod
 
remember that an MCB / RCBO is an 'off load' device and not designed for full load switching, I would put in an isolator as a mater of principle, if only for local isolation for the untrained. mechanical switching.

I can't see as that is right, the MCB/Rcbo is designed to break a fault current which would be several times the flc. Table 53.2 lists a 60898 for isolatin, emergency and functional switching
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Do I need an isolator?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
cornburn,
Last reply from
truckster,
Replies
13
Views
10,513

Advert

Back
Top