just wondering what the deal is if you change say a old style re-wire able C.U to a board with 1 rcd covering all circuits? (providing all bonding and testing is ok)

does this comply to the regs?
would this be passed by a scheme?

by doing this you have made the board a lot safer

i know normally you would either use a dual rcd or put in rcbo's to minimise the inconvenience if there was a fault (e.g tripping the ring takes everything out)

also where do you stand if for whatever reason the customer doesn't want 2 RCD's/ RCBO's??

thanks in advance
 
any circuit with cables buried in walls without earthed metallic protection require RCD. if you are installing a new CU it must be to current regs. i.e.17th. so, in 9 case out of 10, you need to fit as a minimum requirement, a dual RCD board.
 
No you cannot use a single RCD to protect the whole board this is due to inconvieniant tripping .you need to protect using either a dual RCD board or boards with individual RCBO's , if they want to upgrade its far more benificial to change to a dual RCD board as they should be wired light up sockets down sockets up lights down so if a single RCD trips you dont loose the whole house ,it wouldnt be passed by a scheme as it contraviens the 17th edition regs
 
when have you seen cables chased 2" deep????? ok if in a studded wall, but how can you tell if they are less than 50mm deep? knock a nail in, see if it sparks??
 
agree with telextrix on this one even stud wall are not 50mm as the timbers used in studs are 75 x 50mm so even if dead center 37.5mm so not 50mm ,you are right in saying at a depth of 50mm or more but as blocks and bricks tend to be 75mm the its the same as a stud very difficult to get to meet that unless its a cavity all of course ,then its not that easy as you could have hollow blocks and risk going through the wall
 
Last edited by a moderator:
agree with telextrix on this one even stud wall are not 50mm as the timbers used in studs are 75 x 50mm so even if dead center 37.5mm so not 50mm ,you are right in saying at a depth of 50mm or more but as blocks and bricks tend to be 75mm the its the same as a stud very difficult to get to meet that unless its a cavity all of course ,then its not that easy as you could have hollow blocks and risk going through the wall
37.5 +10 for the board.still under 50.
 
ok so its pretty much set in stone that you need to use either dual rcd or rcbo's. (apart from a couple of scenarios e.g surface mounted lights etc..)

what if you had this set up

20a night storage .... 20a night storage .... 30ma RCD (fed by E7tails) 6a lights ... 20amp undersink w/h ... 32a ring ... 32a cooker ... 32a shower... 30ma RCD... main switch (fed by normal tails)


am i right in saying you would have to put the lights on a RCBO ( for regulation 341)

is there anything stopping you having E7 and normal circuits in one board ?

are night storage heaters bad for earth leakage? would this show up if you did a I.R test between live and earth on the flex connected to the heater or would earth leakage only be present when the element hot?

is it against the regs to use a RCD as a main switch on the E7 (shown above in bold )

cheers for your help much appreciated
 
Last edited:
A single rcd covering the whole of an installation

I have done just that recently

It complies with current regs,"honestly"

For a start,a property can have more than one installation

When it covers the whole of the property,deviations to current regs can be cited,"minimise inconveniance"

I am not so struck with shock and horror when it is mentioned, as many seem to be

Instead of proclaiming that 2 rcds must be used,
It would be interesting to hear of "why" you think there is a need to minimise inconveniance,practically,what is the situation that demonstrates this requirement

If a situation can be given as an example, and other ways of minimising inconveniance can be given,then where lies the "You must have a 2xrcd 17th edition board" (whatever that is supposed to be)

My view on the matter is that they brought in the all encompassing "requirement for rcds for everything in most circumstances" then realised that in practice this was a naive action because of the reality and real world away from the desktop fantasy land

The consequence of the rcd everything,was boards with rcbo's
Expensive and not very accepted because of the cost
It was then dreamed up to have 2 rcds and split the circuits,then cross their fingers this covered the inconveniance issue

The 16th ed. where the split board was in use (and the best system that I have encountered through the different editions) could have been adapted to rcd the special locations and leave the other rcd unpoteced side circuits alone

The fob that is the dual rcd board and accepted as the right thing to have,has only been adapted in spite of its shortfalls ,not because it was the best means of complying with the over the top requirments

Its good to know that they are getting back to reality with some of their proposed changes
 
there are some grey areas when it comes to using rcd, personally i would put a split board and use rcds they are not that expensive its only when you want to use rcbos that gets really xpensive.

better be safe that sorry, use rcd and i think the futture will probably be rcbos on everything.
 
A single rcd covering the whole of an installation

I have done just that recently

It complies with current regs,"honestly"

For a start,a property can have more than one installation

When it covers the whole of the property,deviations to current regs can be cited,"minimise inconveniance"

I am not so struck with shock and horror when it is mentioned, as many seem to be

Instead of proclaiming that 2 rcds must be used,
It would be interesting to hear of "why" you think there is a need to minimise inconveniance,practically,what is the situation that demonstrates this requirement

If a situation can be given as an example, and other ways of minimising inconveniance can be given,then where lies the "You must have a 2xrcd 17th edition board" (whatever that is supposed to be)

My view on the matter is that they brought in the all encompassing "requirement for rcds for everything in most circumstances" then realised that in practice this was a naive action because of the reality and real world away from the desktop fantasy land

The consequence of the rcd everything,was boards with rcbo's
Expensive and not very accepted because of the cost
It was then dreamed up to have 2 rcds and split the circuits,then cross their fingers this covered the inconveniance issue

The 16th ed. where the split board was in use (and the best system that I have encountered through the different editions) could have been adapted to rcd the special locations and leave the other rcd unpoteced side circuits alone

The fob that is the dual rcd board and accepted as the right thing to have,has only been adapted in spite of its shortfalls ,not because it was the best means of complying with the over the top requirments

Its good to know that they are getting back to reality with some of their proposed changes

Elderly lady in bed 1st floor RCD trips house plunged into darkness trips and falls down the staires trying to get to the CDU to reset the RCD, and thats the reason why a single RCD shouldnt be used . This was given as an example by the NIC and i have come across this situation when the exact thing has happend
 
Last edited by a moderator:
Elderly lady in bed 1st floor RCD trips house plunged into darkness trips and falls down the staires trying to get to the CDU to reset , and thats the reason why a single RCD shouldnt be used . This was given as an example by the NIC and i have come across this situation when the exact thing has happend
a good argument for emergency lighting in all homes of the elderly. along with mains smoke detectors. sfaety of vunerable people should take priority over cost IMO. be a better use of government grants than filling attics with itchy muck that should be banned anyway.
 
Last edited:
Must admit i do do that in very vunerable elderly peoples propertys now this was after the lady in question 86 and fell down the stairs breaking her hip ,luckely she survived the fall but she'll never walk properly again
 
Elderly lady in bed 1st floor RCD trips house plunged into darkness trips and falls down the staires trying to get to the CDU to reset the RCD, and thats the reason why a single RCD shouldnt be used . This was given as an example by the NIC and i have come across this situation when the exact thing has happend


Elederly lady with rcbo populated board,supplied by a credit or coin meter
Lack of funds.whole of supply disconnected,

Elderly lady with either rcd over whole of installation or rcbo or Twin rcd board with emergency lights
She manages for a little while, whilst situation resolved

Inconveniance is subjective

The possible loss of supply is a much bigger priority than the type of board, if the elderly ladies welfare and safety was the main priority

Instead of being horrified by the single rcd board.I believe that emergency lights for new installations are the better option and by far the best means of minimising inconveniance
 
I agree Des and your comments made a very good point emergency lighting would be a far better idea ,your right about credit meters to they will cut off so makes a big farce about dual RCD / RCBO boards
 
was talking to my doc the other day and he was telling me a case where an elderly lady fell on the stairs because she reckoned the energy saving bulb, she had just switched on, was so dim at start up that she missed her footing ! But at least it was using less energy :rolleyes:
 
Interesting discussion chaps......personally whilst I dont throw a wobbly over a single RCD...it has to be a very bad idea given that the least little thing takes them out, and not everyone is able to follow simple fault isolation proceedures to get it to reset till the sparks arrives. It strikes me that if you want to rcd everything for absolute safety then two rcd's are better than one,common sense innit?
Dual RCD boards are a step forward from split load IMO if RCBO's are cost prohibitive....E/lights?...there's defo a case for one adjacent to the CU being compulsory on new build or major refurbs.
 

Reply to do you have to fit a dual rcd board in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
807
  • Question
Link between the neutral bars will need to be a bit more than an offcut of 2.5mm2 as well. Link needs to be rated at the full capacity of the CU.
Replies
3
Views
1K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
I should have written more…. 😫 😂😂
Replies
5
Views
1K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks