Do you have to run separate earth with SWA which is supplying a D/B | on ElectriciansForums
Discuss Do you have to run separate earth with SWA which is supplying a D/B in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
E
electricshock
Do you have to run separate earth with SWA which is supplying a D/B.
Ive done the tests and the steel wire is good enough for earth.
This job was done last year.
Its for an industrial EICR
if the armour is adequate as regards csa and satisfies adiabatic. perfectly OK.
trhere's a stcky... can i use the armour... good read.
Reply to Do you have to run separate earth with SWA which is supplying a D/B in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...