This may seem like a stupid question but when testing for continuity using the long lead method I know you test the water and gas bonds etc but do you test the incoming earthing cable. I ask this because reading guidance note 3 it talks about the earthing conductor to be tested and I am slightly confused as I was never shown a test on the main incoming earth at college and have yet to see an electrician perform this. If so what is the process


Really hope i can get an answer and cheers for anyone who responds
 
When doing your Ze test you will also be confirming continuity of the main earthing conductor.
 
I have on the odd occasion tested continuity between the incoming cable sheath of a TN-S supply, and the MET - and found it was surprisingly high - due to a loose and corroded clamp that I wasn't prepared to tighten myself.
 
It’s the first test you do after completing safe isolation.

Remove the earth cable from the MET and test for continuity between the end of it and where it terminates on the earth bar in the CU. Once verified, replace cable into MET, then proceed to test bonding of water, gas, any supplementary bonding etc...

It’s also verified when testing Ze, but that’s a live test and you’d want to verify continuity of protective conductors prior to that while dead testing an installation.
 

Reply to Do you test the continuity of an installations main incoming earth in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
488

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top