Hi
I've been asked to install a power supply for a sun bed in a salon:
Sunbed is 60 x 225w lamps = 13.5K
Divide 230v = 59amps
Table 4D2A:
10mm T&E 63amp capacity clipped direct.
I'm installing a dedicated CU with a 63a MCB and isolator fed via a henley block on the meter tails for the sunbed to avoid the basement studio being plunged into darkness!
So far so good.
I haven't got paperwork for the sunbed but I understand that the ballasts typically have an earth leakage current of 75ma which increases over time. So 30ma RCDs can't be used. 100ma are not recommended for shock protection.

Am I required to protect this circuit with an RCD?

Thanks
Steve
 
IMO, an RCD is not required as long as the cable is not buried in a wall <50mm deep. however, i'd be measuring Ze and calculating Zs and PEFC to ensure that the cpc in 10mm T/E was adequate.
 
Thanks for the quick responses, much appreciated.
The manufacturer, Sunquest's (Aurora) website has very basic information unfortunately.
Client bought the most powerful model before taking advice on the power requirements of course. Luckily only a 3 metre run to the board.
2 guys coming down from Leicester crack of sparrow f**t to install expecting everything to be ready...
Regards
Steve
 
All installed now.
Blokes who installed it both had tanning parlours in Leicester. They reckoned just a couple of vents needed. No fan. Cabinets are used 6 mins at a time.
See how it goes, not the easiest place to install a ventilation duct.
Cheers Steve
 
All installed now.
Blokes who installed it both had tanning parlours in Leicester. They reckoned just a couple of vents needed. No fan. Cabinets are used 6 mins at a time.
See how it goes, not the easiest place to install a ventilation duct.
Cheers Steve

Qualified for the job then lol. Did you end up sticking it on a RCD?
 

Reply to Does a sunbed require RCD? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top