I've been asked to install a power supply for a sun bed in a salon:
Sunbed is 60 x 225w lamps = 13.5K
Divide 230v = 59amps
Table 4D2A:
10mm T&E 63amp capacity clipped direct.
I'm installing a dedicated CU with a 63a MCB and isolator fed via a henley block on the meter tails for the sunbed to avoid the basement studio being plunged into darkness!
So far so good.
I haven't got paperwork for the sunbed but I understand that the ballasts typically have an earth leakage current of 75ma which increases over time. So 30ma RCDs can't be used. 100ma are not recommended for shock protection.
Am I required to protect this circuit with an RCD?
Thanks
Steve