Wasn't really a question, more of an observation that DurhamSparky said a L-E fault would blow the OCPD quickly as the fault current would be great. This isn't completely true on a circuit with a high Zs as the fault current would be lower, hence the reliance on an RCD.

I dont fully agree with the wording there JUD:eek:
Surely the earth fault curent would be low,but the Short circuit current is usually no different to a Tn system for bumping out the ocpd

The overcurrent on a Tn is more important Zs wise than it is on a TT
The RCD and RCBO s electronics dont like high fault currents apparantly and are not as reliable as on a TT system
The Tn system with an RCD is not as reliable for the function of the RCd as a TT system
OR so I was told :)
 
I dont fully agree with the wording there JUD:eek:
Surely the earth fault curent would be low,but the Short circuit current is usually no different to a Tn system for bumping out the ocpd

If you read my post again, you'll notice that I said a L-E fault (line to earth) on a circuit with a high Zs (Earth fault loop impedance) would not blow the OCPD in the required time but an RCD would.

No mention of short circuit (L-N) which should still have a high enough fault current to blow the OCPD. :)
 
Last edited by a moderator:
No mention of short circuit (L-N) which should still have a high enough fault current to blow the OCPD. :)

I would agree if the Zs was just over the limits, but not so much if it was ridiculously high, as long as the circuit is T&E.

As the neutral is larger than the CPC, obviously the impedance would be lower on the neutral-line loop. But if it was a ridiculously high Zs, i.e. a couple of Ohms over, then I would be measuring the line-neutral loop to make sure that it is low enough to produce enough fault current to trip the device in the required time....
 

Reply to Does an RCBo or RCD cover the requirements in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
684

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top