lofty84

A circuit is protected by a BS88 fuse and the prospective fault current is 171 A. How do I determine the csa of the CPC assuming 70 oC themoplastic cables with copper conductors.

Can anyone tell me where I need to be looking in the BS 7671 or onsite guide please ?

I think it might be page 128 in the onsite guide but Im not 100 %

thank you
 
reg 543.1.4 of BS7671 don't think it is in OSG

edit you need to know the size of the fuse as well as the type (if my brain is in gear)
 
Last edited by a moderator:
anyone brave enough to attempt to see if this is right ?

A water heater with an output of 5kw is connected to a 230v supply via a bs 60898 type b protective device. the cable is 70 oC PVC insulated thermoplastic coper conductors and the length of cable is 18m. the ambient temperature is 35oC. The cable runs for 300 mm through thermal insualtion. it runs together with one other cable for most of its length and is clipped direct to the wall. Determine the following and show all calcs and refs to tables.

1. Design Current

Ib = 5000/230 = 21.73 A

No diversity according to the on site guide (page 97)

Minimum protective device rateing

In is greater then or equal to Ib = 25 A mcb BS 60898

Correction Factors

It ? = In/caxcgxcixcc

ca=table 6a OSG/ cg = table 6c OSG/ ci = i think table 6b OSG/ cc = 1 i think page 124 OSG ??

It = 25 / 0.94 x 0.80 x 0.51 x 1 = 65.18 A

not sure what do do or say for the minimum cable rating ??

Minimum cable size

= 10mm2

Maximum allowable voltage drop

= 4.4 according to table 6D on page 130 OSG

Actual Voltage Drop

= (mv/a/m) x ib x l / 1000

= 4.4 x 21.73 x 18 / 1000

= 1.72 A

is it 5 % of 230 (11.5) so yes that means it doesnt need a bigger cable ?
 

Reply to DOes anyone know how to do this in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top