Does BS7671 allow fuse rating to exceed cable rating where it is not required to offer overload protection ??

As in the case of a 100A fuse/16mm tails: supplying a CU with just a few final rcbo circuits ?
 
The supplier’s fuse is not there to protect any part of a consumer’s installation.
It’s there to protect the supplier’s equipment.

A consumer’s installation begins at the consumer connection point at the meter.
BS7671 applies to the consumer’s installation not the supplier’s network.
As far as BS7671 is concerned, there is no 100A fuse.
That said, if the supplier agrees, their fuse can be used to protect part or all of a consumer’s installation.
 
Could you give me any pointers ? Reg numbers ?
The best practise guide (number 6 I think -consumer unit replacement) states in section 6.1 that 16mm meter tails with a 100A cutout could be deemed adequate if the maximum demand of the installation does not exceed the ccc of the tails AND also that the requirements of Regulation 434.5.2 for protection of the tails against fault current are met.

To meet the requirements of the above regulation with 16mm tails on a 100A fuse Ze needs to be 0.48 or less. Therefore 'in theory' a TNCS should always be ok with 16mm tails. A TNS would be ok if Ze less than 0.48. Not sure about a TT but K sqared x S squared is never going to be > I squared x t so I guess its not acceptable for a TT.
 
Last edited:
Ps... can someone please tell me how to write a sqaured sign on an android device? Also an ohm! I used to be able to do it but the hash thing doesnt work any more!:(
 
Does anyone actually contact the supplier to confirm anything with them like ever??
Will their fuse protect our tails, can we extend our tails greater than 3meters, do we have any special considerations to think about when applying protective bonding in a pme installation other than using bs7671 etc?
 
... if the maximum demand of the installation does not exceed the ccc of the tails AND also that the requirements of Regulation 434.5.2 ... Not sure about a TT but K sqared x S squared is never going to be > I squared x t so I guess its not acceptable for a TT.
Hi - the earth fault current for TT is very low. With typical Ze ranging 10 to 100 Ohms the earth fault current won't bother 16mm tails :)
 
Does anyone actually contact the supplier to confirm anything with them like ever??
Will their fuse protect our tails, can we extend our tails greater than 3meters, do we have any special considerations to think about when applying protective bonding in a pme installation other than using bs7671 etc?

I have a few times. Once I rang 'em and was passed on to an engineer. I was asking if their supply was TN-C-S, 'what's that in English, do you mean PME?', and I've pulled your main fuse, sealed it (no Pinnipeds jokes please) with one of your sticky temporary seals; I've got the seal number etc for you, 'errgh what, seal number, ??'.

On the first instance, the engineer came out to inspect the head, said it can be converted to PME, just do it yourself. :)
 

Reply to Does BS7671 allow fuse rating to exceed cable rating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
635
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top