Carl86

DIY
Joined
Oct 28, 2021
Messages
3
Reaction score
1
Location
Coventry
I'm buying a house and have received the electrical testing certificate. There were two C1's and a C2 identified, all very easy fixes even for an amateur DIYer, the problem I have is that the electrics were condemned for this reason and so the busbar was removed from the consumer unit. This also seems a very simple task that I'd happily undertake but I just need to know wether this kind of work would need to be undertaken and signed off by a professional or the implications of not getting it done professionally if any...I've attached some pictures of the faults which as I said are very cheap and easy fixes and don't really warrant the call out and first hour charge of a professional if I can get away with it.
 
TL;DR
If an amateur is able to fix C1 faults easily, can they also reinstall a busbar that is removed as electrics condemned for the C1 faults? Or does this need to be signed off?

Attachments

  • [ElectriciansForums.net] Does reinstallation of busbar need professional sign off?
    Screenshot_20211028-224737.jpg
    192.7 KB · Views: 31
  • [ElectriciansForums.net] Does reinstallation of busbar need professional sign off?
    Screenshot_20211028-224941.jpg
    233.2 KB · Views: 32
  • [ElectriciansForums.net] Does reinstallation of busbar need professional sign off?
    Screenshot_20211028-224731.jpg
    156.8 KB · Views: 32
  • [ElectriciansForums.net] Does reinstallation of busbar need professional sign off?
    Screenshot_20211028-224703.jpg
    155.6 KB · Views: 28
Presumably it's not being rented out? In which case a 'satisfactory' EICR is not a requirement - unless your insurance demands it, which doesn't seem to be common (as yet at least).

Do you mean that the seller had the busbar removed before selling the property? Or that an electrician has done so on their own basis when carrying out an EICR for you?

In my opinion, that's not something they should have done unless it was agreed by you in advance. Electricians do not have the same rights as gas fitters to 'condemn' appliances that are working (Though there are methods to isolate dangerous circuits or draw attention to risks)

None of the issues on the list appear to be that complicated, and are certainly within the remit of a good DIY'er..

It would be useful to have a way of testing that the socket is working when reinstalled though - and that the ring final circuit (if present) has been maintained.

With respect to the busbar, IMO, since this is not installing a new Consumer Unit, it would not need to be notified under Part P of the building regulations, so there is no legal requirement for it to be done by a 'professional'.

However, it is vital that it is done correctly, with the terminals clamping with suitable torque at each point. It is something that can be done wrongly quite easily, and that could quite easily lead to a dangerous situation with poor connections causing heat damage or in worst case, a fire.

Personally, unless you have experience of doing similar work I would consider the cost of a professional to replace the busbar and check all the terminals are tight well worth the outlay, for peace of mine alone. Even if it is to check what you have already done.

If you want to use the EICR for future use, then having someone do the work and putting it on paper may be beneficial. However, in theory as long as the remedial work is 'documented' then you have met the requirements.

OOI, what code was given to the pendant with flex showing? According to the Best Practice Guide, "use of unsheathed flex for lighting pendant" is a non compliance but one that does not have to be reported, so not even a C3. Having said that, it should be changed anyway, even if only because it looks nasty!


TL;DR. It could be done by a DIYer, but the busbar is probably best left to someone with at least experience of ensuring tight connections...
 
Thanks for the response.
The seller is a housing association and the property unoccupied, they carried out the assessment and had the busbar removed which they stated is normal practice if there are any imminent dangers present. The flex showing on the pendant was given C2 which I think was harsh as an exposed live in such a location would probably warrant the same but hey ho, an easy fix.
Appreciate your comments on having a spark do the busbar reinstatement, I was thinking along the same lines it just seemed a lot of faff for what is essentially a 5 minute job but you can't put a price on your family's safety I suppose.
 
Thanks for the response.
The seller is a housing association and the property unoccupied, they carried out the assessment and had the busbar removed which they stated is normal practice if there are any imminent dangers present. The flex showing on the pendant was given C2 which I think was harsh as an exposed live in such a location would probably warrant the same but hey ho, an easy fix.
Appreciate your comments on having a spark do the busbar reinstatement, I was thinking along the same lines it just seemed a lot of faff for what is essentially a 5 minute job but you can't put a price on your family's safety I suppose.
To be fair to them, single insulated cables elsewhere are definitely a C2, just that the pendant case seems to be specifically mentioned separately - I guess because older pendants had a twisted flex without a sheath. In your case most likely the cores have either not been placed correctly over the strain relief tabs internal to the pendant base, or they've broken. That's definitely a DIY job either way.

I wonder if there may be legal implications of them effectively selling a house without a functioning electrical system and if that was clearly defined in the sale documents etc, but given the complications of conveyancing as it is not sure that would go anywhere...

It's certainly possible for someone with even basic skills to install a busbar correctly - but it's also very easy with many makes of MCBs to get the busbar incorrectly positioned on the wrong side of the screw terminal so that it appears to be tightly fitted, but is actually not...

Leading to things like this happening:

[ElectriciansForums.net] Does reinstallation of busbar need professional sign off?

Use of a mirror underneath the busbar when positioning it can help. It needs care and obviously an understanding of the dangers of holding a large metal piece inside a box with always on mains power to it! (since an external isolator is a rarity).

But with some ringing around I would have thought you could easily find someone able to do it for well under £50 (depending on location), which is money well spent for peace of mind I'd say.

There is an argument that in reinstalling it, all the circuits need to be tested to be safe to energise, but since you have the EICR then there shouldn't be a huge issue with that.

Was the busbar left on site do you know?
 
To be fair to them, single insulated cables elsewhere are definitely a C2, just that the pendant case seems to be specifically mentioned separately - I guess because older pendants had a twisted flex without a sheath. In your case most likely the cores have either not been placed correctly over the strain relief tabs internal to the pendant base, or they've broken. That's definitely a DIY job either way.

I wonder if there may be legal implications of them effectively selling a house without a functioning electrical system and if that was clearly defined in the sale documents etc, but given the complications of conveyancing as it is not sure that would go anywhere...

It's certainly possible for someone with even basic skills to install a busbar correctly - but it's also very easy with many makes of MCBs to get the busbar incorrectly positioned on the wrong side of the screw terminal so that it appears to be tightly fitted, but is actually not...

Leading to things like this happening:

View attachment 91425

Use of a mirror underneath the busbar when positioning it can help. It needs care and obviously an understanding of the dangers of holding a large metal piece inside a box with always on mains power to it! (since an external isolator is a rarity).

But with some ringing around I would have thought you could easily find someone able to do it for well under £50 (depending on location), which is money well spent for peace of mind I'd say.

There is an argument that in reinstalling it, all the circuits need to be tested to be safe to energise, but since you have the EICR then there shouldn't be a huge issue with that.

Was the busbar left on site do you know?
The house was very much "sold as seen" being a housing association they have little knowledge of the house specifically and must just follow set policies for unsatisfactory eicr. They have left the busbars taped to the CU. As long as I fix the 2 face plates and the blanks in the DB then at least it will be safe to restore power so I can get on with some other jobs.
 

Attachments

  • [ElectriciansForums.net] Does reinstallation of busbar need professional sign off?
    Screenshot_20211029-005702.jpg
    206.8 KB · Views: 21

Reply to Does reinstallation of busbar need professional sign off? in the DIY Electrical Advice area at ElectriciansForums.net

Similar threads

If you're having new circuits, then a new consumer unit would be highly recommended. One rcd covering the whole installation isn't a good idea...
Replies
2
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top