D dustman Joined May 21, 2022 Messages 9 Reaction score 0 Location Tucson, AZ Jun 4, 2022 #1 Running #8 to AC condensor. Does the ground wire need to be #8 as well?
Megawatt - Staff member Arms Supporter Joined Jul 22, 2019 Messages 3,042 Reaction score 1,830 Location North Carolina USA Jun 5, 2022 #2 dustman said: Running #8 to AC condensor. Does the ground wire need to be #8 as well? Click to expand... No after you exceed 30 amps then you can start derating your equipment ground so in your case you can pull # 10 wire for your equipment ground. Upvote 0 Downvote
dustman said: Running #8 to AC condensor. Does the ground wire need to be #8 as well? Click to expand... No after you exceed 30 amps then you can start derating your equipment ground so in your case you can pull # 10 wire for your equipment ground.