A mobile van converted into office with circuits supplied from a 3000w inverter and to a 3 position change over switch to a ccu with rcd protection .the cable from c/o switch is a 2.5mm2(iz 27A) to the ccu and circuits are as follows
1 16a mcb supplying heater 1000w on a 1.5mm2 cable
2 16a mcb supplying one socket outlet 1.5mm2 cable
3 16a mcb supplying a sfs for kettle 1.5mm2 cable
4 6a mcb supplying 3 lights. 1.5mm2 cable
the changeover switch can only supply one circuit at a time so the 3000w inverter produces max current approx 12a therefore circuits wired in trunk so realistically the criteria ib<in<iz is met because 1.5mm2 cable current carrying capacity is approx 21a? (without getting book out) so am unsure whether or not this conforms TO THE REGS?
If it is a caravan then the 1.5mm cable is fine but they have to be to BS EN 60332-1-2 which have to have certain fire propagation qualities Regs 721.521.2 and 721.524.1
If it is a mobile unit then again the cable size is fine, but must be flexible not solid conductors within the unit, and have to be of the low smoke kind. Regulation 717.52
Reply to Does this conform the regs? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...