hi everyone
a second opinion would be appreciated
was called to a house in February as RCD was intermittently tripping. some times 3 times a day sometimes none. during my initial look i discovered when the oven was ran for more then 5 minutes the RCD tripped. my inspection then found a faulty cooker element which was replaced and hey presto no problems any more.
until this morning. same problem.
RCD tripped twice on Monday didn't on Tuesday but did 3 times yesterday. hasn't tripped today either.
i went today for 2 hours today as it was all i could spare. my tests were as followed
starting with a circuit at a time
extension ringmain all meggered clear N - E 299 N - L 299 E - L 299
hot tub supply meggered clear N - E 299 N - L 299 E - L 299
shower meggered clear N - E 299 N - L 299 E - L 299
cooker meggered clear N - E 299 N - L 299 E - L 299
i didn't test 3 circuits as its a big --- 6 bedroom house and didn't want to go around unplugging everything - down ring main - up ring main - kitchen ring main.
i then decided to ramp test the RCD. i disconnected every earth and neutral except the extension sockets which i know are clear. also turned all mcbs off excluding extension(where my megger was plugged into) the RCD tripped at 17mA. the mains RCD is a 30 mA 80 amp crabtree starbreaker split load, i then tested the RCD on half times which tripped the RCD immediately. i tried numerous times. is this RCD faulty? i have more follow up tests to do but don't want to purchase a crabtree RCD without factoring in other causes
like i said i was limited to 2 hours so couldn't do thorough test until next week.
any advice would be helpful
thanks
a second opinion would be appreciated
was called to a house in February as RCD was intermittently tripping. some times 3 times a day sometimes none. during my initial look i discovered when the oven was ran for more then 5 minutes the RCD tripped. my inspection then found a faulty cooker element which was replaced and hey presto no problems any more.
until this morning. same problem.
RCD tripped twice on Monday didn't on Tuesday but did 3 times yesterday. hasn't tripped today either.
i went today for 2 hours today as it was all i could spare. my tests were as followed
starting with a circuit at a time
extension ringmain all meggered clear N - E 299 N - L 299 E - L 299
hot tub supply meggered clear N - E 299 N - L 299 E - L 299
shower meggered clear N - E 299 N - L 299 E - L 299
cooker meggered clear N - E 299 N - L 299 E - L 299
i didn't test 3 circuits as its a big --- 6 bedroom house and didn't want to go around unplugging everything - down ring main - up ring main - kitchen ring main.
i then decided to ramp test the RCD. i disconnected every earth and neutral except the extension sockets which i know are clear. also turned all mcbs off excluding extension(where my megger was plugged into) the RCD tripped at 17mA. the mains RCD is a 30 mA 80 amp crabtree starbreaker split load, i then tested the RCD on half times which tripped the RCD immediately. i tried numerous times. is this RCD faulty? i have more follow up tests to do but don't want to purchase a crabtree RCD without factoring in other causes
like i said i was limited to 2 hours so couldn't do thorough test until next week.
any advice would be helpful