I’m afraid I agree with Stroma. The regs may not be written in the clearest way to avoid confusion or prevarication, but the intention of the regulation in my opinion is clear.

Just a thought, if the OP did that with two lighting circuits to free up some space, why not do it with some other circuits including Rings (loads accepted)?
My understanding of it is a lighting Circuit and then another single lighting point has been added in the loft sounds awfully like a spur taken from an OCPD of a lighting circuit to me
 
Well an FCU contains an OCPD (Fuse).
If I use an FCU to spur off from a circuit, does the fact that there is an OCPD at the origin of the spur, make the spur a separate circuit?
Where does the supply originate from?
The circuits primary OCPD.
Why twist things and be argumentative as per?
 
Ok where’s the OCPD at the origin of an installation?
That depends on how far back to “origin” you want to go? The MCB is an OCPD if it’s an origin of a final CCT. The bs1361 or 88-3 fuse is An OCPD if it’s the origin of a particular installation. The substation fuse, the grids fusing all the way back to the OCPD at the generator...
 
That depends on how far back to “origin” you want to go? The MCB is an OCPD if it’s an origin of a final CCT. The bs1361 or 88-3 fuse is An OCPD if it’s the origin of a particular installation. The substation fuse, the grids fusing all the way back to the OCPD at the generator...
The distribution network is outside of the scope of BS7671.
As the discussion is in relation to an Assessor stating something does not comply with BS7671, I was thinking of the origin as per BS7671.
 
The distribution network is outside of the scope of BS7671.
As the discussion is in relation to an Assessor stating something does not comply with BS7671, I was thinking of the origin as per BS7671.
That’s why I stuck origin in quotation marks in just playing devils advocate ;) sarcastically I may add
 
I'm also interested in why markysparky disagreed with sparkychick's post re lollipop circuits.


Because, as Spin helpfully points out, details on how a circuit is formed is in appendix 15. And as we seem to be so intent on dissecting the regs to the nth degree, there is nothing at all that looks remotely like a ‘lollipop’ circuits in app15. Therefore, if it is not in the regulations of how a circuit should be wired, it is not compliant.
 
The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?
 
The Appendix 15 argument.

Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).

The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"

Options... it is not the exhaustive list of possibilities that comply with 433.1, if it were some of what we do everyday would be non-compliant (like a 20A DP switch feeding a single socket for an appliance wired in 2.5/1.5mm cable - complies with 433.1.204 but isn't on the diagram in appendix 15).

For a ring circuit to comply with the regulations, it must comply with 433.1.204 which defines the acceptable topology of a ring final circuit purely in terms of cable loading. Thus providing the cables are not overloaded in accordance with 433.1.204, a lollipop or ring final circuit will comply.
 
The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?

If course! A C3 if I were doing an EICR.

And how can it be a lollipop and also a ring? What would you put under the continuity tests in an EIC and also if the ‘stick’ end is of a larger size what size cable do you put in the EIC?
 

Reply to Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Locked
Thread closed.
2
Replies
19
Views
881
It does seem to me that there's a capacitively coupled voltage to each set of downlights (on the light side of the switch), and when you put the...
Replies
6
Views
288

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top