Hello!

I am curious as to what the exact rules are in England for carrying out and signing off EICR's.

I am finding different answers across google and various forums, some may be outdated, some may be bullshi.

I myself have over 12 years sparking experience but I am just finishing off my NVQ to be fully qualified. I have come across a job where I would need to do a few EICR's and sign them off for building control. This is well within my capabilities and I would definitely consider myself as competent but, I am just wondering as I have not completed my NVQ neither am I a registered electrician am I "allowed" to carry out and sign the report?

Thanks!
 
There are no specific rules as such, legally anyway. BS7671 says "The periodic inspection and testing shall be carried out by one or more skilled persons competent in such work". And that's it.

You may find the person ordering the report may have their own requirements of you, such as CPS registration, qualifications etc, but that's up to them - check with you local building control. And a good idea to have insurance in place of course.
 

Reply to Doing and signing of an EICR as an improver in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

I did my NVQ a couple of years back now and as I was a sole trader as a mate, I was my employer, so they just let me sign both bits
Replies
1
Views
434
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
951

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top