How would i calculate the overload setting needed for a 3 phase 0.5kw dol motor?
 
Its 3 phase so formula is:
I = kW / ( √3 x pf x VLL ), in kA


For 3 phase Kw to Amps without power factor I divide the Kw rating by 0.692 - the result is in Amps. 0.72A in this case.


and efficiency


better to read the nameplate if possible

if it's a manual starter overload could be 90% of FLA


500w /1.7/400/0.75pf/0.7eff=1.37 amp line current approx
 
Last edited by a moderator:
get the FLA off the rating plate on the motor and set your overload to 110% above that

e.g 10 amp motor 10x110%=11 so set the overload to 11 amps.
 
with pumps, we would even half close the valves, so it was the maximum load that the pumps would have under normal service. The we carried out full commsioning of the water features, so any nuisance tripping would be identified within that time. that rule works well.
 
ya if it's above nuisance level and below FLA it can be don that way:D

motors can be oversized anyway
 
Last edited by a moderator:

Reply to dol starter overload calculation? in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

Similar threads

  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
990
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
612

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top