How would i calculate the overload setting needed for a 3 phase 0.5kw dol motor?
 
Its 3 phase so formula is:
I = kW / ( √3 x pf x VLL ), in kA


For 3 phase Kw to Amps without power factor I divide the Kw rating by 0.692 - the result is in Amps. 0.72A in this case.


and efficiency


better to read the nameplate if possible

if it's a manual starter overload could be 90% of FLA


500w /1.7/400/0.75pf/0.7eff=1.37 amp line current approx
 
Last edited by a moderator:
get the FLA off the rating plate on the motor and set your overload to 110% above that

e.g 10 amp motor 10x110%=11 so set the overload to 11 amps.
 
with pumps, we would even half close the valves, so it was the maximum load that the pumps would have under normal service. The we carried out full commsioning of the water features, so any nuisance tripping would be identified within that time. that rule works well.
 
ya if it's above nuisance level and below FLA it can be don that way:D

motors can be oversized anyway
 
Last edited by a moderator:

Reply to dol starter overload calculation? in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
The wiring looks ok. When you say it trips the breaker, do you mean the MCB supplying the starter? if so what is the rating of the MCB
Replies
6
Views
1K
  • Question
Why are you doing this, you potentially could cause mains transients on smaller power networks and local installations, the reason it has a...
Replies
3
Views
1K
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
842
Thanks Lucien a diagram would be most helpful in the meantime I am going to try and draw out how I have wired the contactors there are no remote...
Replies
3
Views
1K
Hi All, I have recently purchased a motor soft starter from aliexpress for a 3 phase motor Before connecting load I measured the input and...
Replies
0
Views
566

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks