Hi all :).

Seeing alot of cases where I have seen 20A DP switches in a kitchen (for example) each feeding a radial 2.5t&e to each white goods appilance or similar, and the 20A DP switch primarys are fed from the 32A kitchen ring final circuits - Is this accepteble to BS7671?

I'm guessing if it's only serving a 1 gang s/o or 13A fused spur it would not be at risk of overload at the switch?

Please advise.

Many Regards

Jamie
 
OK, so we have a 20A DP control switch with its supply side as a point in an RFC protected at 32A. The load side connects to some accessory, either a single socket outlet or FCU, that will limit the load to 13A by way of the BS1362 fuse. We declare it as a fixed load so the 20A switch is within its thermal (continuous load) rating.

But what happens with a short circuit on the unfused spur? The 20A switch has to survive the fault being cleared by a 32A device without disintegrating, instead of a 20A device. Any accessory intended for use on an RFC will have been designed for that duty, but has the 20A switch? Check with manufacturers? Splitting hairs? Take it one stage further - given suitable cable would it be acceptable to control a 1A fixed load on a 40A circuit, using a bog standard 5AX light switch?

Discuss...

No because you'd never get the incoming 40a rated cable into the switch terminal. :wink:
 
you'd never get the incoming 40a rated cable into the switch terminal.

I chose 40A for this very reason - Bare 2H2.5 MI will do 40A and will fit any decent light switch terminal. Anyway, does the cable need to be rated for 40A inside a panel and carrying a fixed load of 1A?
 
Well let's say a 1mm cable was connected to the outgoing side of this switch feeding a 1 amp load, if there was a short in this section of the circuit the 40a MCB would still disconnect before any other damage was sustained ?
 

Reply to Domestic: 20A DP switches and ring final circuits?? in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
You are allowed to apply a diversity calculation to the cooker circuit, due to the unlikely occurrence of all elements of both appliances being on...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks