Hi all :).

Seeing alot of cases where I have seen 20A DP switches in a kitchen (for example) each feeding a radial 2.5t&e to each white goods appilance or similar, and the 20A DP switch primarys are fed from the 32A kitchen ring final circuits - Is this accepteble to BS7671?

I'm guessing if it's only serving a 1 gang s/o or 13A fused spur it would not be at risk of overload at the switch?

Please advise.

Many Regards

Jamie
 
I would have thought so Paul.

Yes I know, just wanted to "ask" instead of "inform" via a sarcastic format (I'm in that mood tonight). Very good point Dave btw.

Any switch rating is the amount of Amps it can take under normal usage without the contacts over heating/meting/burning via conducting electricity from the main supply to the load.

eg. A 6A light switch on a 10A MCB with a load of 8A.

Q. What do people think will happen in time?
 
Yes I know, just wanted to "ask" instead of "inform" via a sarcastic format (I'm in that mood tonight). Very good point Dave btw.

Any switch rating is the amount of Amps it can take under normal usage without the contacts over heating/meting/burning via conducting electricity from the main supply to the load.

eg. A 6A light switch on a 10A MCB with a load of 8A.

Q. What do people think will happen in time?

Being picky here, but you are saying the load on the 10A MCB is 8A. So that's OK. The 6A light switch will be OK, assuming the load it is switching is less than 10A. But I do get what you were intending to ask :) Daz
 
Being picky here, but you are saying the load on the 10A MCB is 8A. So that's OK. The 6A light switch will be OK, assuming the load it is switching is less than 10A. But I do get what you were intending to ask :) Daz


An 8A load protected by a 10A MCB is absolutely fine. The problem is with an 8A load conducting via a 6A rated switch! The contacts within the switch are over loaded and will quickly get warm then melt or fuse.

The OP's question about the 20A rating of a FCU, the 20A bit is for the load side and not the incoming terminals of the FCU.
 
An 8A load protected by a 10A MCB is absolutely fine. The problem is with an 8A load conducting via a 6A rated switch! The contacts within the switch are over loaded and will quickly get warm then melt or fuse.

The OP's question about the 20A rating of a FCU, the 20A bit is for the load side and not the incoming terminals of the FCU.

Ha ha, I was being picky with the way the question was worded. Not to worry. Daz
 
Yes I know, just wanted to "ask" instead of "inform" via a sarcastic format (I'm in that mood tonight). Very good point Dave btw.

Any switch rating is the amount of Amps it can take under normal usage without the contacts over heating/meting/burning via conducting electricity from the main supply to the load.

eg. A 6A light switch on a 10A MCB with a load of 8A.

Q. What do people think will happen in time?


the light will go out.
 
Ha ha, I was being picky with the way the question was worded. Not to worry. Daz

It's been fun :wink:

the light will go out.

unless the contacts are fused?? (had that problem once on a dimmer switch were the winding's just fused together)

But the switch will start emitting light instead :) Daz

That is a safety feature, glowing switch so you can see where to turn the lights on before walking into a dark room and stub your toe on the coffee table leg! :rofl: done this, my little toe hurt for 3 days!
 
OK, so we have a 20A DP control switch with its supply side as a point in an RFC protected at 32A. The load side connects to some accessory, either a single socket outlet or FCU, that will limit the load to 13A by way of the BS1362 fuse. We declare it as a fixed load so the 20A switch is within its thermal (continuous load) rating.

But what happens with a short circuit on the unfused spur? The 20A switch has to survive the fault being cleared by a 32A device without disintegrating, instead of a 20A device. Any accessory intended for use on an RFC will have been designed for that duty, but has the 20A switch? Check with manufacturers? Splitting hairs? Take it one stage further - given suitable cable would it be acceptable to control a 1A fixed load on a 40A circuit, using a bog standard 5AX light switch?

Discuss...
 
OK, so we have a 20A DP control switch with its supply side as a point in an RFC protected at 32A. The load side connects to some accessory, either a single socket outlet or FCU, that will limit the load to 13A by way of the BS1362 fuse. We declare it as a fixed load so the 20A switch is within its thermal (continuous load) rating.

But what happens with a short circuit on the unfused spur? The 20A switch has to survive the fault being cleared by a 32A device without disintegrating, instead of a 20A device. Any accessory intended for use on an RFC will have been designed for that duty, but has the 20A switch? Check with manufacturers? Splitting hairs? Take it one stage further - given suitable cable would it be acceptable to control a 1A fixed load on a 40A circuit, using a bog standard 5AX light switch?

Discuss...

No because you'd never get the incoming 40a rated cable into the switch terminal. :wink:
 
you'd never get the incoming 40a rated cable into the switch terminal.

I chose 40A for this very reason - Bare 2H2.5 MI will do 40A and will fit any decent light switch terminal. Anyway, does the cable need to be rated for 40A inside a panel and carrying a fixed load of 1A?
 
Well let's say a 1mm cable was connected to the outgoing side of this switch feeding a 1 amp load, if there was a short in this section of the circuit the 40a MCB would still disconnect before any other damage was sustained ?
 

Reply to Domestic: 20A DP switches and ring final circuits?? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top