Just been asked to do some work at a house with a 3phase supply. 1 phase supply's the main consumer unit for the house, and the other 2 phases go into an off peak meter then into an old contactor before supplying two separate single phase consumer units for storage heating. My question is should the whole system be isolated by 1 main 3phase switch? (At the moment it relys on the main switch in each CU to isolate each phase individually)
 
Does it really need 3 phases mate? You could save your client a good bit of cash and earn massive amounts of brownie points here.
Ideally there would be isolation for each live conductor preferably in one unit so you didn't have to mess around looking for it
 
No long meter tails!

I always thought that if you have a 3phase supply you should be able to isolate it from one switch. If there is a main D B then the incomer would act as this or if you have a busbar you would require a main switch. In this case I have one phase each going to a seperate consumer unit albeit 2phases via a contactor so wasn't sure if it should be isolated by one main 3 phase switch, a 2 phase and a 1 phase switch or as it is now 3 seperate single phase switches.

On page 45 of OSG it says that in a TNCS 3phase system (which this is) an isolator must interrupt the line conductors at the origin of the installation.

Technically this has been achieved through 3 seperate isolators.....still not sure
 
The requirement to provide a main switch relates to the installation, not to the number of phases.
537.1.4: "A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation."...
What you have to my mind would be considered as two installations.
One installation for the peak side of things, and the other for the off peak.
Obviously whoever made the installation, considered it to be three installations.
What would be your thoughts for instance, if the building were split into three flats, with each flat being supplied by a single phase?
 

Reply to Domestic 3phase supply in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
211
462 excerpt below. The incoming supply is via a electrical plant room to the block of flat, each flat has a standard DNO cutout fuse but no...
Replies
9
Views
904
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
147
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
665

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks