...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed

And the question is?
 
the CU tails are tri-rated and will withstand higher currents than the same csa of 7 strand, notwithstanding that they may have a higher max. temperature, which should be limited to the temp. rating of the main switch/RCD/s etc.
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed
oh man!!
lol...lol...
what happens to current in parallel circuits eh eddie?
 
Your forgetting that their are normally doubled up sets, one set to each of the RCD units thus the load is shared down 2 sets of 16mm... as above the cable is tri-rated and unless you know the manufacturer then you cant gage its rating which well come down to 3 factors
-Core arrangement
-Size
-insulation
 
As above any wholesalers will supply it but its use may have restrictions like panel wiring etc as its insulation has differing properties...
 
have used tri-rated for meter tails in the past (coz. it was free from where i worked). bear in mind you need to fit crimps to the ends.
 
...what if you had a 100a cutout?!

So for e.g your tails (consumer and dist.) are both 25mm2 and you have a cutout fuse that is 100a - technically the cutout fuse is the only thing protecting from itself to the bottom of your mcbs. Most consumer units have the "built in" cables that are 16mm2 (from bottom of main switch to top of RCDs) - The CCC of these cables is 85/87ish amps so isnt that a problem?!

I'm curious!

Thanks

Ed

I wouldn't worry your head about it, not just because of the internal configuration of dual RCD CU's, but the fact you'll probably never see 100A being drawn through a typical domestic/commercial CU. ...I know that i never have, and not even close either!! lol!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Domestic CUs have built in wiring of 16mm2 but...
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Eddiesparks,
Last reply from
Amp David,
Replies
15
Views
2,200

Advert

Back
Top