So in our new house theres a washing machine.
It seems to work fine. It's plugged in to a plug socket in the kitchen
Whenever I turn it on, it goes for a minute or two then trips the MAIN house circuit breaker (not the local circuit circuit breaker).
When I take an extension lead and plug it in to another socket in a different room, it runs the cycle fine and doesnt trip anything.
Doenst make much sense to me...I'm sure this is a simple thing to sort out - but not for me.
This Circuit breaker that trips after a few minutes, that would be the Residual Current Device( RCD)
When you pug it in via an extension lead, it works fine all right so far?
What you may have is a Consumers Unit (fuse board) that has some circuits that are protected by the RCD and some that aren't, your washing machine must have an earth fault possible a N to E fault, that's my diagnoses from afar and without any test equipment, you may need the assistance of a white goods engineer.
Can we assume that the ring final circuit socket in another room is protected by another RCD ?. Have you tried initial start up of washing machine in extension lead ?, if it then trips then it could be the washing machine. It could be two things with the 1st ring 1.existing leakage currents from other appliances and by a bit more has put the value over the threshold 2. fault /damage to circuit cable.
or could be a N-E reversal on the kitchen socket. soon as the heater kicks in, drawing a larger current, the load is across L -E, thus tripping the RCD.
try kettle direct into kitchen socket without extension lead. it's possible that the extension lead has a missing or damaged cpc.( earthing conductor ).
Sounds to me like there may be a marginal fault contact in the washing machine socket, or its supply, which leaks enough current to trip only when the washing machine electronics connect a decent sized load.
I would replace the washer ?
could well have a leak to ground,
A common thing with washers.
I'd test the entire system for a N-E fault first, if the OP replaces the washer and the problem persists he's wasted his money and will still have to employ the services of a sparks. Get an experienced electrician to carry out an insulation resistance test on the electrics first, probably cost an hour labour.
QUOTE - [ Sounds to me like there may be a marginal fault contact in the washing machine socket, or its supply, which leaks enough current to trip only when the washing machine electronics connect a decent sized load. ] END QUOTE .
Surely it should not leak any current, at any time, regardless of load ?
Reply to Domestic electric puzzle in the Domestic Electrician Forum area at ElectriciansForums.net
You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...