Hello im after some advice please.

A friend of mine had asked me to hook up a Domestic Generator for him.

My plan is to install a change over switch next to
the meter with obviously mains supply in load side out to the consumer unit. Then run some 4mm armoured cable from a 32amp commando socket outside into the Gen side of the change over switch.

My question is what else do i need to do?

What about the earthing arrangment? As i assume the DNO dont want you to connect to their earth incase of a fault when they are working on the system.

Does the changeover switch disconnect the MET when switched over to Generator?

Do i need to install an earth rod next to the Generator?

Looking at a 6kva genny


Thanks for any advice.
 
Last edited by a moderator:
Hello im after some advice please.

A friend of mine had asked me to hook up a Domestic Generator for him.

My plan is to install a change over switch next to
the meter with obviously mains supply in load side out to the consumer unit. Then run some 4mm armoured cable from a 32amp commando socket outside into the Gen side of the change over switch.

My question is what else do i need to do?

What about the earthing arrangment? As i assume the DNO dont want you to connect to their earth incase of a fault when they are working on the system.

Does the changeover switch disconnect the MET when switched over to Generator?

Do i need to install an earth rod next to the Generator?

Thanks for any advice.
depends on the generator, be very careful which generators you use.

most are fine for lights etc but connect a pc and can get pproblems
 
Further information I've just spoken to the manufacture of the change over switch i am looking at.

I asked them if it disconnects the main earth from the system when switched over to generator and they said it doesn't.

So im wondering what is the correct thing to do with the earthing arrangement?

thanks.
 
Hello im after some advice please.

A friend of mine had asked me to hook up a Domestic Generator for him.

My plan is to install a change over switch next to
the meter with obviously mains supply in load side out to the consumer unit. Then run some 4mm armoured cable from a 32amp commando socket outside into the Gen side of the change over switch.

My question is what else do i need to do?

What about the earthing arrangment? As i assume the DNO dont want you to connect to their earth incase of a fault when they are working on the system.

Does the changeover switch disconnect the MET when switched over to Generator?

Do i need to install an earth rod next to the Generator?

Looking at a 6kva genny


Thanks for any advice.

First of all, you need to install an external commando plug, not socket. This is very important, for reasons which I'm sure when you think about it will become obvious :)

Secondly, I'd advise that you read up on section 551.

If you post your location you may find someone on here who will be able to help. It seems to me that you lack knowledge in this area and there are a number of things that are crucial that you get right, from generator selection to earth referencing. You will need the correct type of changeover switch and there are certain strict procedures that need to be followed that you will have to inform the customer of so that if ever they need to transfer from mains to back up power they can do it safely and without damaging equipment. There will almost certainly be a need to open up the generator and adapt the connections within (this will need confirmation from the manufacturer that it won't void the warranty).

If you aren't 100% sure what you're doing, get help.

Get this just a little bit wrong and you'll have a death trap on your hands.
 

Reply to Domestic Generator Change Over Switch in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
Afternoon! Hoping someone has experience working on the ABB gear below. It’s in a Mobile Office/ Welfare unit, supplied via either 230v hook up...
Replies
0
Views
568
  • Question
just read 712.551 👍 (and a few other characters)
    • Like
Replies
9
Views
2K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
378
Replies
1
Views
628
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
529

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks