T
Thai Amateur
At last I've been able to complete theelectrical installation of the bungalow. Taken so long because I'vehad to fix so many problems with the building work left by my earlierlocals.
So now I've done some preliminarytesting and YES I am going to get a local professional in to do thefinal testing but I want to make sure that I haven't made any majorerrors. Plus I want to make sure that any local I get really doesknow how to test properly.
I have a Kyoritsu model 6010A multitester.
1. Tested continuity – OK.
2. Tested conductor resistance R1 + R2.Compared result with recommended length of cable for voltage dropmultiplied by the resistance for the cable size. Problem with spurs Iadded to water pump and car port but overcame this with anothercircuit. All R1 + R2 well within the recommended parameter.
3. Test Insulation (at 500v).
Here I seem to have a problem althoughI can't see why. I have 2 consumer units supplied from a single main(3 pole) disconnecter switch.
First I connected L-N and tested L-E.
Unit 1 – 160 Mohms
Unit 2 – 80 Mohms
Next I removed the link and tested L-N,L-E, N-E.
Unit 1
L-N - 0.11 MOhms
L-E – 140 MOhms
N-E – 195 Mohms
Unit 2
L-N - 0.08 MOhms
L-E – 60 MOhms
N-E – 70 Mohms
First time I've done anything like thisso any advice would be most appreciated.
So now I've done some preliminarytesting and YES I am going to get a local professional in to do thefinal testing but I want to make sure that I haven't made any majorerrors. Plus I want to make sure that any local I get really doesknow how to test properly.
I have a Kyoritsu model 6010A multitester.
1. Tested continuity – OK.
2. Tested conductor resistance R1 + R2.Compared result with recommended length of cable for voltage dropmultiplied by the resistance for the cable size. Problem with spurs Iadded to water pump and car port but overcame this with anothercircuit. All R1 + R2 well within the recommended parameter.
3. Test Insulation (at 500v).
Here I seem to have a problem althoughI can't see why. I have 2 consumer units supplied from a single main(3 pole) disconnecter switch.
First I connected L-N and tested L-E.
Unit 1 – 160 Mohms
Unit 2 – 80 Mohms
Next I removed the link and tested L-N,L-E, N-E.
Unit 1
L-N - 0.11 MOhms
L-E – 140 MOhms
N-E – 195 Mohms
Unit 2
L-N - 0.08 MOhms
L-E – 60 MOhms
N-E – 70 Mohms
First time I've done anything like thisso any advice would be most appreciated.