Paul117

Hi all. I have my inspection tomo to join NICEIC as a domestic installer.

On my main job to be inspected, a board change, my r1 + r2 doesn't marry up with the Ze and zs. Parrerlel earth path somewhere I guess as r1 + r2 is very low. Does this need to me found to satisfy the nic man or will a knowledge of the situation suffice.

Thanks
 
might just be that you are measuring Zs on no-trip. some MFTs will give a higher reading than the true one, due to only pushing 15mA into the circuit.
 
Hi all. I have my inspection tomo to join NICEIC as a domestic installer.

On my main job to be inspected, a board change, my r1 + r2 doesn't marry up with the Ze and zs. Parrerlel earth path somewhere I guess as r1 + r2 is very low. Does this need to me found to satisfy the nic man or will a knowledge of the situation suffice.

Thanks
Jesus! He won't like that at all, better cancel it asap and sort it out!
 
Sarcasm mr monkey. It is an mft tester on 2 wire no trip. Could be the cause. Just though the boiler is on the ring could explain it.
Yeah sorry mate couldn't resist, its really easy as long as you're competant and can display your testing skills, he probably won't pay too much attention to the anomoly as long as you've got the chocolate hobnobs out :)
Just for future reference its R1+R2, r1 is end to end of live on a ring and r2 is end to end of earth
 
congrats. and @ guitarist, the meggers give reasonably accurate readings on no trip. i checke mine at home on hi i got 0 95 ohms and on no trip, 1.07
 

Reply to domestic installer inspection in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
863
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
478
That was in relation to UNG's solution of changing to a type B MCB rather than type C to fix the "problem" I would be concerned about any...
Replies
14
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks