Hi, I don't know if anyone can help with this. A customer called me out saying that a British Gas boiler service had highlighted a socket showing >2000 on the EFLI test. I went to look and got 1.12 on one side of the (two gang) socket and >2000 on the other. I assumed it was a dodgy socket and replaced it.

Testing the replacement I'm now getting about 1.15 as a loop test when the socket's off the wall but >2000 once I screw it in. I can't find any voltage on the back box.

Any ideas please?
 
All I can think of is a dodgy connection on the different test lead or plug adaptor thingy. So you are getting decent-ish reading on the conductors, but a crap reading through a new socket, so have assumed you are using an additional test adaptor or a change of leads to do that test.
 
The initial fault sounds strange as it is difficult to disconnect the earthing from one side of socket but I suppose it is possible, it is more likely (but still unlikely) to have been a damaged earth connector at the socket, e.g. pushed to one side by the plug pin.

Once the socket front has been replaced I woudl assume that there is a poor connection to the earth terminal, perhaps the sleeving is caught on the screw, such that when the conductors are moved as the socket is screwed back the earth disconnects. This would be much more likely if both cpcs are in the same terminal or there is an earth discontinuity on one leg of the ring.
 
Sounds like the first socket must have been faulty. But the change as the socket is screwed in must be a break in the CPC (s) surely?
 
This whole thing dont make sense. If the boiler is on own radial then it has a spur yes? Where does the socket come into it? But anyway clearly the earth makes and breaks when the wires are in different position. And anyway a socket tester will not give you an ohmic measurement. Confused I am.
 
The socket tester that BG used was probably one of those that give a very rough idea of efli: there is one that has measurements something like <1; <5; >5 ohms. So when BG 'measure' it, there is no leeway for TT earthing.

To the OP, is the socket on a stud wall with a socket on the other side of the wall perhaps. The act of screwing back the face plate could be pushing the cable/conductors at an adjacent socket out of position.

Also test the R1 value with the face plate back, as it could be that and not the R2 causing the issue. Although I would suspect the CPC to be the cause.
 
He could also have a social life unlike us sad sacks.:confused:
 

Reply to Domestic socket loop test puzzle. in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top