Hi all. - Sorry - bit of an essay below but would appreciate time taken to read.

Have been asked to look at wiring an extension on a farm house. Took a look and found the following:

Supply is 1ph via the 3ph supply on the other side of the stock yard. feed to house through a 1361 60/80A to 60A RCD (ancient and the test button doesn't trip it) throught a 60A semi enclosed into 10mm (I think - although the cable cross section is oval not round so not that easy to tell) SWA to the house and into a 100A Isolator into MCBs. Currently the Main Earth to the House is TN-S exported via the outer of the SWA.

The farmer is not about to rip up his stock yard and under the newish barn to run a 16mm SWA so I'm stuck with the 10mm. Therefore 60A max supply.

I need to replace the old RCD but can only find 63A which is outside the rating of the SWA. Any smaller and his 5 bed house is going to be short on Amps.

I'm thinking of making the house TT and only using the TN-S to protect the supply cable.

Any suggestions as to where I can get a 60A RCD and MCB (or RCBO)? OR any other solutions??

Many thanks
 
Hiya mate, an rcd is only for fault current not overcurrent so would have to be switchfuse or rcbo, and if it is 10mm and the start of the cable is over the other side of the stock yard you may have too much volt drop so will have to reduce the current anyway
 
As markysparky said - I should have read the post correctly:eek:

Whats the length of run , Is it buried, whats the earth loop at the house DB, and max demand / design current
 
Hi All.

The SWA is buried under the stock yard and barn. RCD necessary because the farmer has already put one of the support posts for the barn through the SWA. and the way he swings his JCB around, I can't gurantee that a bucket won't go through it again. Fuse needed for over current protection to the cable in case of fault.

Run is about 40m and I've checked the vd already and is only 1.2%.

I like the 63A RCD put through a 60A fuse. Yes I was getting confused between cable protection (RCD) and over current protection(fuse).

Am I doing the right thing by putting the House on TT and leaving the cable protected by TN-S?

Thanks

Sorry didn't read the last post fully.

Haven't done earth loop for house yet. Design current with diversity only about 50A - I've convinced him he needs to change the 9kW shower for a 13A pump version.
 
Last edited:

Reply to Domestic supply on a farm in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
660
  • Question
Your electrician can't do it. The dno has to do it, and it will be entirely at your expense. Be careful moving anything as mentioned above older...
Replies
3
Views
3K
I'm planning to build a shed in the far RH corner of the rear garden. It will have a reinforced concrete base, wood structure, flat roof and be...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks