Hi all. - Sorry - bit of an essay below but would appreciate time taken to read.
Have been asked to look at wiring an extension on a farm house. Took a look and found the following:
Supply is 1ph via the 3ph supply on the other side of the stock yard. feed to house through a 1361 60/80A to 60A RCD (ancient and the test button doesn't trip it) throught a 60A semi enclosed into 10mm (I think - although the cable cross section is oval not round so not that easy to tell) SWA to the house and into a 100A Isolator into MCBs. Currently the Main Earth to the House is TN-S exported via the outer of the SWA.
The farmer is not about to rip up his stock yard and under the newish barn to run a 16mm SWA so I'm stuck with the 10mm. Therefore 60A max supply.
I need to replace the old RCD but can only find 63A which is outside the rating of the SWA. Any smaller and his 5 bed house is going to be short on Amps.
I'm thinking of making the house TT and only using the TN-S to protect the supply cable.
Any suggestions as to where I can get a 60A RCD and MCB (or RCBO)? OR any other solutions??
Many thanks
Have been asked to look at wiring an extension on a farm house. Took a look and found the following:
Supply is 1ph via the 3ph supply on the other side of the stock yard. feed to house through a 1361 60/80A to 60A RCD (ancient and the test button doesn't trip it) throught a 60A semi enclosed into 10mm (I think - although the cable cross section is oval not round so not that easy to tell) SWA to the house and into a 100A Isolator into MCBs. Currently the Main Earth to the House is TN-S exported via the outer of the SWA.
The farmer is not about to rip up his stock yard and under the newish barn to run a 16mm SWA so I'm stuck with the 10mm. Therefore 60A max supply.
I need to replace the old RCD but can only find 63A which is outside the rating of the SWA. Any smaller and his 5 bed house is going to be short on Amps.
I'm thinking of making the house TT and only using the TN-S to protect the supply cable.
Any suggestions as to where I can get a 60A RCD and MCB (or RCBO)? OR any other solutions??
Many thanks