Ryan_Moore

Hi Sparks!
I am hoping to become an apprentice very soon and I have a question for you all,
What is the difference between the 230v single phase used in domestic buildings and the 415v used in commercial/industrial buildings. Also why is it necessary for there to be a difference, what are the pros and cons of each.


Also I have heard rumours of all new builds now having electric heating, does this mean less work for plumbers and gas fitters and more work for us....or you I should say at the moment, give me a few years :)
 
Last edited by a moderator:
Each phase is 230V, If connected together on a motor for example or by cross connection by fault it will then become 415V. I haven't explained it very well but that's the basics of it. You will learn all about it once you start your apprenticeship, good luck and ask any questions if/when you get stuck.
 
Hi Sparks!
I am hoping to become an apprentice very soon and I have a question for you all,
What is the difference between the 230v single phase used in domestic buildings and the 415v used in commercial/industrial buildings. Also why is it necessary for there to be a difference, what are the pros and cons of each.


Also I have heard rumours of all new builds now having electric heating, does this mean less work for plumbers and gas fitters and more work for us....or you I should say at the moment, give me a few years :)
How long have you got :)

You mentioned an interview in the pm. So I'll try and answer this in terms of a level of knowledge they could reasonably expect you to have.

The main difference between them, as you've probably guessed, is the single versus three (poly) phase. That's probably what they are looking for you to comment on.

Remember that voltage is derived from a difference in potential between two points. In single phase that's between line nominal voltage (230V) and neutral (practically 0V). The word nominal is used because in reality the voltage isn't 230, neither does it stay constant, it fluctuates over time between around 230V and around 240V (and can change if you measure it quickly in succession).

With any (single/poly phase) AC supply the voltage fluctuates a number of cycles per second (Hertz). In the UK that's 50 times a second, in the USA it's 60 times a second. The change from +Ve to -Ve over time would plot a near perfect sine wave (ignoring the voltage fluctuation).

What you get with 3 phase is 3 of those sine waves starting approximately 1 Second / 50 Hertz / 3 Phases) apart from one another IE 0.0067 Seconds (or 6.7 Milli Seconds).

So with 3 phase you get the option of either using one phase only, with the Potential Difference derived between a phase and neutral. Or you can chose to derive the voltage between two phases (which is where the nominal 415V is derived from). The nominal 415V is derived from 240V times the square root of 3 (240V was our old nominal voltage).

With 3 phase you can get away with using (3) smaller sized (cheaper!!) cables, rather than using one large cable capable of handling larger currents driven by a 415V source.

The upshot is it's not "necessary" per se, but certainly cheaper and more flexible.

So 3 phase, some pros/cons, by no means an exhaustive list ;) :

Pros: More power is available to drive power hungry devices like plant/machinery (anything with a motor).

Cons: 3 phase arguably more dangerous (they'll expect you to cite the health/safety issues).
 
Thanks very much both of you, the interview I have this time next week(more or less) have asked me to speak for 3 minutes on the reason behind the difference in voltage of domestic and industrial.

So a 3 phase is 3 times that of a single phase, obviously, for something that requires alot of power to run ( Like the shutter in the wholesalers I work in) it pulls some power from each of the phases to opperate, because if it tried to opperate on 1 phase, it would blow the 60A main fuse, right?
 
Last edited by a moderator:
Thanks very much both of you, the interview I have this time next week(more or less) have asked me to speak for 3 minutes on the reason behind the difference in voltage of domestic and industrial.

So a 3 phase is 3 times that of a single phase, obviously, for something that requires alot of power to run ( Like the shutter in the wholesalers I work in) it pulls some power from each of the phases to opperate, because if it tried to opperate on 1 phase, it would blow the 60A main fuse, right?
Not 3 times, but more power available. I would avoid saying it would blow the fuse, it may (depends on a number of factors, ambient temperature and other considerations).
 
I believe this is one of those questions where the answer can be never ending.
In general power is generated and distribute as 3 phase. Typically every 3 houses will be fed 1 phase from a 3 phase supply cable in the street. Every third house being on the same phase.
Each phase is 230V to earth or neutral, but is 400V between phases.
Where an installation is expected to have a high current demand, such as some shops, blocks of flats, factories etc. all 3 phases will be fed to the installation.
Equipment that uses 3 phases as opposed to single phase, is more efficient.
If you consider a large engined motorcycle traveling at 70mph, the engine will just ticking over, hardly any strain at all.
Wheras a small engined motor cycle will be revving it's nuts off at the same speed.
Sorry have to go.
 
Lot of maths in that description, I like it, bit of a maths nerd B-)
I am sure between now and my interview I will have alot of questions, I gotta get this apprenticeship!
I really am grateful of any and every bit of help you can offer and I will let you know how it goes.
 
Lot of maths in that description, I like it, bit of a maths nerd B-) I am sure between now and my interview I will have alot of questions, I gotta get this apprenticeship!I really am grateful of any and every bit of help you can offer and I will let you know how it goes.
Once you've done your research for this 3 minute talk on 3 phase motors post up what you are going to say and we will have a look at it for you and see if there is anything you've missed out. Hope you get the apprenticeship.
 
Ryan_J_Moore;329180[B said:
]Lot of maths in that description, I like it, bit of a maths nerd [/B]B-)
I am sure between now and my interview I will have alot of questions, I gotta get this apprenticeship!
I really am grateful of any and every bit of help you can offer and I will let you know how it goes.


Do yourself a favour and mention your interest in maths during the interview

When you start ingesting electrical theory,a large proportion of that theory requires a lot of use of maths, and a good understanding of it

It is the conerstone of electrical theory, from the very basic, to the higher levels probably attained by those who responded to your questions
 
As you like maths (mad fool) if you're up on your trig, you can use Sin(2pi x freq x time) to plot out what happens on the fluctuating voltage over time for each of the 3 phases, convert that to a current (assuming resistance of 1 Ohm). Then add up the current across all 3 phases at each point in time and amaze yourself that no current is flowing in the neutral ! :) That's one of the other advantages to a (perfectly) balanced 3 phase system.

With tau = 2pi (for all the newbie nerds).

Voltage at point in time t would be 230V * Sin(tau x 50Hz x t)

Assuming you have access to a spreadsheet.
 
Voltage at point in time t

Isn't "Instantaneous value",easier for us to say when we are drunk
icon7.png
 
I trust for the benefit of Ryan J Moore,that was the only post you made that was a little short on the truth :8:

icon7.png
I have to say I've been good ... haven't posted any obviously misleading information for a long time. ;) (It's been alleged I have a wicked sense of humour ... don't know where anyone would get that idea from). :D
 
Maths question: the sine graph passes through 0 and peaks at 1 and -1 on the y axis, applying this to our electricy stuff, it would pass through 0 ( ie no volts at no time) and peak at 240 and -240 right?

On a single phase this is fine, you have 1 sinx graph and that is that, however when you have 3 phases you end up with 2 translations of the sine graph along with the original, if you translate sin by (-90,0) (I think it my translations arent great) you get the graph of cosx so on 1 axis you have sinx,sin(x+a) and cosx. and each of these represents a phase? At any time(any x value) you have 3 possible solutions(one per graph)

you know what I am gettin too much into this, I need to be patiant and wait til I am actually a apprentice, I am too damn excited now!
 
I have to say I've been good ... haven't posted any obviously misleading information for a long time. ;) (It's been alleged I have a wicked sense of humour ... don't know where anyone would get that idea from). :D
With a tag that says "children on backseats cause accidents, accidents on backseats cause children" I think that is an awesome sense of humour :D
 
Maths question: the sine graph passes through 0 and peaks at 1 and -1 on the y axis, applying this to our electricy stuff, it would pass through 0 ( ie no volts at no time) and peak at 240 and -240 right?

Yes, but remember that's just a voltage that's present. It has to be measured between that point and somewhere else, either 0 volts or one of the phases to derive the potential difference and hence be able to drive a current (remember it's Alternating Current we're interested in, not the voltage).

On a single phase this is fine, you have 1 sinx graph and that is that, however when you have 3 phases you end up with 2 translations of the sine graph along with the original, if you translate sin by (-90,0) (I think it my translations arent great) you get the graph of cosx so on 1 axis you have sinx,sin(x+a) and cosx. and each of these represents a phase? At any time(any x value) you have 3 possible solutions(one per graph)

Stick to using Sin, that's all you need. The phases are 120 degrees out of phase with each other. If we label them P1 P2 and P3 then when P1 is at 0 degrees, P2 will be at 120 degrees and P3 at 240 degrees.


you know what I am gettin too much into this, I need to be patiant and wait til I am actually a apprentice, I am too damn excited now!
Keen is good :D ... just don't come across as hyper or impatient in the interview ;)
 

Reply to Domestic Vs Industrial in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Solved
An NVQ is a vocational qualification and is based upon your work experience and what you put into your portfolio for your assessor to judge you...
Replies
4
Views
715
Thanks mate for the advice, this is just what I was looking for. I think I’ll have to put some thought into the domestic route due to the NVQ and...
Replies
2
Views
242
  • Question
Hi, I’m an industrial electrical engineer apprentice working at a wastewater treatment plant, I’ve been really enjoying the job which I’ve been...
Replies
0
Views
872
  • Question
I don't think it will work with only one stake unless some meters have different operating parameters. It doesn't necessarily have to be a stake...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks