I am hoping to become an apprentice very soon and I have a question for you all,
What is the difference between the 230v single phase used in domestic buildings and the 415v used in commercial/industrial buildings. Also why is it necessary for there to be a difference, what are the pros and cons of each.
Also I have heard rumours of all new builds now having electric heating, does this mean less work for plumbers and gas fitters and more work for us....or you I should say at the moment, give me a few years
How long have you got
You mentioned an interview in the pm. So I'll try and answer this in terms of a level of knowledge they could reasonably expect you to have.
The main difference between them, as you've probably guessed, is the single versus three (poly) phase. That's probably what they are looking for you to comment on.
Remember that voltage is derived from a difference in potential between two points. In single phase that's between line nominal voltage (230V) and neutral (practically 0V). The word nominal is used because in reality the voltage isn't 230, neither does it stay constant, it fluctuates over time between around 230V and around 240V (and can change if you measure it quickly in succession).
With any (single/poly phase) AC supply the voltage fluctuates a number of cycles per second (Hertz). In the UK that's 50 times a second, in the USA it's 60 times a second. The change from +Ve to -Ve over time would plot a near perfect sine wave (ignoring the voltage fluctuation).
What you get with 3 phase is 3 of those sine waves starting approximately 1 Second / 50 Hertz / 3 Phases) apart from one another IE 0.0067 Seconds (or 6.7 Milli Seconds).
So with 3 phase you get the option of either using one phase only, with the Potential Difference derived between a phase and neutral. Or you can chose to derive the voltage between two phases (which is where the nominal 415V is derived from). The nominal 415V is derived from 240V times the square root of 3 (240V was our old nominal voltage).
With 3 phase you can get away with using (3) smaller sized (cheaper!!) cables, rather than using one large cable capable of handling larger currents driven by a 415V source.
The upshot is it's not "necessary" per se, but certainly cheaper and more flexible.
So 3 phase, some pros/cons, by no means an exhaustive list
:
Pros: More power is available to drive power hungry devices like plant/machinery (anything with a motor).
Cons: 3 phase arguably more dangerous (they'll expect you to cite the health/safety issues).