Just thought I would check to see how things are going as I have not heard from you.
Kind regards
Victor
Bonjour Victor.
I did try to pm you but said you were not accepting pm's.
I have been to France and installed first fix.
On arrival discovered there was no existing cu, just a plastic jb where all final circuits were connected to incoming tails from a mere 30A supply/500mA rcd.
I have installed first fix using plastic flexible conduit and singles. The supplier we sourced material from sold rolls of pre-wired plastic conduit coming in various sizes.
I have installed a many-ways board with protection split between 30mA type A and 30mA type AC RCD's and double pole circuit breakers.
The existing earth electrode was inaccessible and gave about 300 ohm reading. I Installed two new electrodes and main earthwire achieving a 100 ohm reading in dry conditions.
The research I carried out suggested that line and neutral should be red and blue, switched lives orange, two-way strappers as black and green/yellow for earth.
I used a similar theme to England for all bonding.
We will be requiring an upgrade in supply in order to cope with the demands of electric heating etc.
Any comments, advice or suggestions appreciated.