If you meter tails of 25mm goes into a CB and comes out in 16mm to the CU can the 16mm earth dropped down to 10mm at this point or should it stay at 16mm. (this is a PME system). i'm looking in the regs but isn't clear to me
 
if its rated at 63a then 16mm tails 10mm earth and 6mm bonds would suffice although for the costs that would be incurred i would replace with 25, 16, 10 respectively.

I've looking at that table and what i understand it as is if the line is 16mm the earth must also be 16mm?
as widdler stated if you use the adiabatic then you will find the earth size will come out considerably smaller

fault current= uo/ze
s= rootsquare isuared x t / k
 
Last edited by a moderator:
the main point to note on these often asked questions is that a lot of books provide examples where main incoming fuse is rated at 100a which in majority of cases it wont be in which case you now have to look at wether costing or safety is the issue to the client, if you can size your cables and protection and back it up with calculation then your signature on the Eic proves you are competent in the case of an inquiry.
 

Reply to domestic in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top