Hey guys I see this now and again on my rounds....8.5kw method C on 2 x 2.5mm cable......does it state anywhere in the regs that it a radial must be a single cable Or is it acceptable ? the very least i think its lazy not using 6mm but as always I'm well off from the more experienced guys think ;)

Thanks

[ElectriciansForums.net] doubled cable on a radial
 
Sounds like a guess. If its not in BS7671 and you can tget information from the manufacturer then you will be guessing.

Although 2.5mm is rated around 27A (clipped direct and depending on its run), the ring will not necessarily put equal load on each cable and hence the 32A device. In your case the cables may well be the same length and therefore in theory should split the load equally. But this does not take into account resistance at the terminations. again this is an unknown. in the event that one side comes free, a 32A MCB will be just enough to protect the cable. In your sitaution it will not be and you will have a fire.

You cant back yourself up in a court case with guesswork. If you go by BS7671 then you will not have unknowns and you will not be guessing. No one will be able to argue.
 
unorthodox but no problem at all using 2 feeds to a fixed equipment so long as they're the same length ( for load balancing reasons ) and both cables are wired into the same terminals at the CU ( for identification purposes )
 
While these smaller cables are not normally used in parallel single point supplies, the same principles still apply!! So in fact, those 2 X 2.5mm cables, will carry more current than a 6mm cable using the correct installation method!! So long as all the required criteria for a parallel supply is adhered too, then no problem!! lol!!


Parallel supply/feeders are more commonly used with the larger sized cables, where they can significantly increase CCC with reduced size of cables, and can generally be run over longer distances, than the use of a single much larger sized cable!!
 

Reply to doubled cable on a radial in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
875
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top