Doubling up on cables to increase csa. | on ElectriciansForums

Discuss Doubling up on cables to increase csa. in the Australia area at ElectriciansForums.net

T

Tillywolves

Hi everyone. Im a fire alarm guy, who was qualified as a spark, over 27 years ago, to the 15th edition.

Just fitting a new alarm system into a kids nursery school, and noticed that a new consumer unit had been fitted since I first quoted the job. The spark has doubled up two 10mm earth singles to make it over the 16mm needed.

Can this be ok, or does it have to be a single cable only.

cheers in advance.

Tilly


(any questions on fire alarms I'd be happy to answer);)
 
Yes but only if both cables are identical follow the same run hence the same length, if for any reason you suspect the load isnt balanced between them then it not ok.
 
Last edited by a moderator:
agree ,I just assumed that the guy didnt want to rip out the existing cable so just improved on what was there, but he might have took a diferent route
Has to be same length usually same route as this makes sure loading is split equally the calculations of having same csa but different lengths isnt recognised by regs thus not allowed although it might be mathematically safe.
I will stand corrected but i do recall the regs have a clause about paralleling cables up and that they must follow each other and be the same length.
 
Last edited by a moderator:
The regs do comment on parallel conductors in chapter 43 section 433.4, which then refers you to other parts of the regs. Though they are really aimed at LIVE conductors, under fault conditions you need the earthing conductor to be capable of carrying the possibilty of high currents.

Technically nothing wrong with doubling up on an earthing conductor, it's like so much in the industry it's deemed not good practice. I suppose if a connection broke at a termination on the MET then it could leave the remaining smaller conductor to carry those high fault currents.
 

Reply to Doubling up on cables to increase csa. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top