Hello all,
Went to fix a problem last week: 'lounge lights not working'. Found 7x50W ELV downlights had been installed with individual 20-60W transformers wired off a single 400W standard dimmer.
The dimmer had blown, along with most of the transformers and on nearly every light fitting, one of the two connector terminals on the 12V side (i.e., that between the transformer and the lamp holder) had overheated and melted the surrounding block. The fittings were safely located away from joists in a generous ceiling space with no insulation.
I replaced all the transformers , along with the connector block 'stand-off' holders and the dimmer and installed 35W lamps and labelled each fitting 'MAX 35W'.
I haven't seen this much damage before in a single circuit and was trying to deduce the sequence of events which led to this. Obviously most people would agree that loading 350W onto a 400W resistive dimmer is overload. Some even won't load more than 50%. Do you reckon this was the only cause or may have there been another factor involved?
Went to fix a problem last week: 'lounge lights not working'. Found 7x50W ELV downlights had been installed with individual 20-60W transformers wired off a single 400W standard dimmer.
The dimmer had blown, along with most of the transformers and on nearly every light fitting, one of the two connector terminals on the 12V side (i.e., that between the transformer and the lamp holder) had overheated and melted the surrounding block. The fittings were safely located away from joists in a generous ceiling space with no insulation.
I replaced all the transformers , along with the connector block 'stand-off' holders and the dimmer and installed 35W lamps and labelled each fitting 'MAX 35W'.
I haven't seen this much damage before in a single circuit and was trying to deduce the sequence of events which led to this. Obviously most people would agree that loading 350W onto a 400W resistive dimmer is overload. Some even won't load more than 50%. Do you reckon this was the only cause or may have there been another factor involved?