Was looking a a job today in a kitchen, the customer had 12 gu10 50w 240v mains downlighters off one switch, 6amp mcb to 1.5cm T&E. Then had a thought ,yes it does happen?
12 lights x 50watts = 600
______ = 2.608 amps
230 v
She has asked for 12 more gu10 50w 240v which will take it to 1200w /230v = 5.217amps all fine but on the same circuit 4 100amp ceiling roses which takes it to 1600w ,so 6.956 amp so greater that the fuse.Yes can use diversity so below 6 amp but should I recommend some light get down rated.Hope I got my maths right as been a long time since school.But she then asked about all 24 lights on one switch where she has 2gang it the moment ,would this trip the mcb due to sudden inrush when the switch opens to 24 gu10.She will not have Elv 12v ones as the transformers can never be replaced or hidden due to the nature of the customers requests.Yes I know its special location.
12 lights x 50watts = 600
______ = 2.608 amps
230 v
She has asked for 12 more gu10 50w 240v which will take it to 1200w /230v = 5.217amps all fine but on the same circuit 4 100amp ceiling roses which takes it to 1600w ,so 6.956 amp so greater that the fuse.Yes can use diversity so below 6 amp but should I recommend some light get down rated.Hope I got my maths right as been a long time since school.But she then asked about all 24 lights on one switch where she has 2gang it the moment ,would this trip the mcb due to sudden inrush when the switch opens to 24 gu10.She will not have Elv 12v ones as the transformers can never be replaced or hidden due to the nature of the customers requests.Yes I know its special location.