tomodo
-
Hi i am installing 6 2x70w light fittings in a factory, as its a long run I have wired six kliks outlets in 2.5mm singles, I am now deciding if the 3 core 1.5mm flex I have is suitable for the klik plug ends that will supply each light. I am putting on a 10amp breaker so that should be sufficient, but I have read in the kliks online manual that you could wire the kliks in 2.5mm and put on a 16amp breaker then have each light fitting on a 1mm flex, they say this is allowed because overload is not possible as its only feeding 1 light and is only allowed to feed one light and if its a short circuit than the current will be more than high enough to trip the mcb. What do people think of this? thanks