Assuming that is the table that details all of the different switching and isolating devices and what they can/can't be used for then I know perfectly well what it says about the subject.

I still won't have MCBs installed as the only means of isolating a machine on my watch though.

Yes mate, that the one.
Fare comment, but for 3 meters of SWA cable then I'm saying it can be used. (within reason)
 
The length and type of cable is irrelevant!
An mcb is a protective device, an isolator is a means of isolation.

What Im saying is that it can be used as an isolator. It all depends on other factors if you want an additional isolator in the circuit nearer to the equipment its feeding.
 
For maintenance purposes having a separate isolator that can e locked off in case of fault or servicing on the machine... you can't have a service engineer coming to replace, repair mechanical parts of the drill then be expected to remove the cover of the DB to remove the cable from the mcb... switching off would not be adequate isolation on its own .... if their was a safety protocol in place where the DB was always padlocked and under control of 1 person only then possible argument but really not a situe' to be in in the first place.

Isolator on the wall adjacent to the drill is the common standard practice and allows for correct lockable isolation to any trade that needs to isolate the drill without the need for them to Electrically trained.
 

Reply to Downsizing Cable ? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
757
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
608
The repair kit is actually sold by WAGO for that specific purpose (in the wall repair). I had wondered myself about shrinking individually first...
Replies
4
Views
765

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top