I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like to give their views on the requirements if any, for the retention, updating and provision of electrical drawings requirements for inspection and testing purposes as required under IEE Wiring Regulations. This in respect of commercial installations. My copy of the IEE Wiring Regulations, albeit only seventeenth edition incorporating amendment 1:2011 has references within regulations as follows:
132.13 Documentation for the electrical installation.
Every electrical installation shall be provided with appropriate documentation, including that required by Regulation 514.9, part 6 and where applicable part 7.
514.9 Diagrams and documentation
514.9.1 A legible diagram, chart or table or equivalent form of information shall be provided indicating in particular:
I. The type and composition of each circuit (points of utilisation served, number and size of conductors, type of wiring), and
II. The method used for compliance with regulation 410.3.2, and
III. The information necessary for the identification of each device performing the functions of protection, isolation and switching, and its location, and
IV. Any circuit or equivalent vulnerable to a typical test
For simple installations the foregoing information may be given in a schedule. A durable copy of the schedule relating to a distribution board shall be provided within or adjacent to each distribution board.
My copy of the IET Guidance note 3 Inspection and testing, IET Wiring Regulations BS 7671:2008 incorporating amendment 1:2011 also indicates the following:
3.6 Required information.
It is essential that the inspector knows the extent of the installation to be inspected and any criteria regarding the limit of inspection. This should be recorded.
Enquiries should be made to the person responsible for the electrical installation with regard to the provision of diagrams, design criteria, type of electricity supply (and any alternative supply) and earthing arrangements.
Diagrams, charts or tables should be available to indicate the type of composition of circuits, identification of protective devices for shock protection, isolation and switching and a description of the method used for fault protection.
3.8.2 Process – prior to carrying out inspection and testing
….. Also, the extent of previous maintenance, routine tests and documentation, including the original design and Electrical Installation Certificate, should be established.
3.8.3 General procedure
….
6.2.1 Where diagrams, charts of tables are not available, a degree if exploratory work may be necessary so that inspection and testing can be carried out safely and effectively; this may include a survey to identify switchgear, control gear and the circuits they control.
Indeed, for more involved installations without diagrams or charts the client should be advised that such diagrams require producing prior to inspection and testing commencing. Alternatively, the inspection can commence in cases where the inspector feels that it is safe to proceed (this may be limited to a visual inspection); the production of diagrams and charts can be called for on the Electrical Installation Condition Report.
I appreciate that this has been updated in the Regulations.
The statements above are open to interpretation but I recall watching a training video on inspection and testing maybe 25 years ago and recall the need for as-built drawings to be made available. I’d therefore appreciate the views of others on this, maybe from an accreditation agency, though publications from the NICEIC seem to be largely straight from the regulations.
Links such as this one Electrical maintenance: the importance of good practice - IET Electrical - http://electrical.------.org/wiring-matters/60/electrical-maintenance/index.cfm entitled Electrical maintenance: the importance of good practice also state the following:
It is vital for both designers and construction teams to recognise the importance of the O&M Manual that they pass on to the maintenance team when they leave site. This is an integral part of the project completion process. However, it is often left until the last minute and rushed, leading to mistakes. By the time the construction team produce their as-built drawings the design team have moved on to the next job. Drawings and documents do not always get the rigorous review they need to ensure accuracy. The advent of Building Information Modelling (BIM) may improve this situation in terms of up-to-date information being produced as the project develops, but that remains to be seen. In the meantime, most projects will follow traditional patterns with the inevitable gaps in continuity in the flow of information.
I explain to my contractors that I want to avoid both my customers and the electricians from encountering an electrical hazard and want to improve electrical safety management for all as well as I am able to. For instance poor asset records is mentioned on Importance of effective electrical safety management - IET Electrical - http://electrical.------.org/wiring-matters/58/esm/index.cfm and the availability of drawings are likely to be part of the risk mitigation in safety management.
Looking forward to your views.
132.13 Documentation for the electrical installation.
Every electrical installation shall be provided with appropriate documentation, including that required by Regulation 514.9, part 6 and where applicable part 7.
514.9 Diagrams and documentation
514.9.1 A legible diagram, chart or table or equivalent form of information shall be provided indicating in particular:
I. The type and composition of each circuit (points of utilisation served, number and size of conductors, type of wiring), and
II. The method used for compliance with regulation 410.3.2, and
III. The information necessary for the identification of each device performing the functions of protection, isolation and switching, and its location, and
IV. Any circuit or equivalent vulnerable to a typical test
For simple installations the foregoing information may be given in a schedule. A durable copy of the schedule relating to a distribution board shall be provided within or adjacent to each distribution board.
My copy of the IET Guidance note 3 Inspection and testing, IET Wiring Regulations BS 7671:2008 incorporating amendment 1:2011 also indicates the following:
3.6 Required information.
It is essential that the inspector knows the extent of the installation to be inspected and any criteria regarding the limit of inspection. This should be recorded.
Enquiries should be made to the person responsible for the electrical installation with regard to the provision of diagrams, design criteria, type of electricity supply (and any alternative supply) and earthing arrangements.
Diagrams, charts or tables should be available to indicate the type of composition of circuits, identification of protective devices for shock protection, isolation and switching and a description of the method used for fault protection.
3.8.2 Process – prior to carrying out inspection and testing
….. Also, the extent of previous maintenance, routine tests and documentation, including the original design and Electrical Installation Certificate, should be established.
3.8.3 General procedure
….
6.2.1 Where diagrams, charts of tables are not available, a degree if exploratory work may be necessary so that inspection and testing can be carried out safely and effectively; this may include a survey to identify switchgear, control gear and the circuits they control.
Indeed, for more involved installations without diagrams or charts the client should be advised that such diagrams require producing prior to inspection and testing commencing. Alternatively, the inspection can commence in cases where the inspector feels that it is safe to proceed (this may be limited to a visual inspection); the production of diagrams and charts can be called for on the Electrical Installation Condition Report.
I appreciate that this has been updated in the Regulations.
The statements above are open to interpretation but I recall watching a training video on inspection and testing maybe 25 years ago and recall the need for as-built drawings to be made available. I’d therefore appreciate the views of others on this, maybe from an accreditation agency, though publications from the NICEIC seem to be largely straight from the regulations.
Links such as this one Electrical maintenance: the importance of good practice - IET Electrical - http://electrical.------.org/wiring-matters/60/electrical-maintenance/index.cfm entitled Electrical maintenance: the importance of good practice also state the following:
It is vital for both designers and construction teams to recognise the importance of the O&M Manual that they pass on to the maintenance team when they leave site. This is an integral part of the project completion process. However, it is often left until the last minute and rushed, leading to mistakes. By the time the construction team produce their as-built drawings the design team have moved on to the next job. Drawings and documents do not always get the rigorous review they need to ensure accuracy. The advent of Building Information Modelling (BIM) may improve this situation in terms of up-to-date information being produced as the project develops, but that remains to be seen. In the meantime, most projects will follow traditional patterns with the inevitable gaps in continuity in the flow of information.
I explain to my contractors that I want to avoid both my customers and the electricians from encountering an electrical hazard and want to improve electrical safety management for all as well as I am able to. For instance poor asset records is mentioned on Importance of effective electrical safety management - IET Electrical - http://electrical.------.org/wiring-matters/58/esm/index.cfm and the availability of drawings are likely to be part of the risk mitigation in safety management.
Looking forward to your views.