Hi,
Since getting back into the trade a few years back have installed controllers for boilers with room stats etc & the odd new S plan system - infrequently & admit I am not well versed in heating controls though can follow a circuit diagram!
Customer has asked me to install a Drayton digistat RF3 to his current set up on a Vaillant ECOTEC plus boiler feeding an S plan heating & water. This system is currently ran from a Drayton LP722 dual channel controller & has never had a room stat connected - purely on/off via controller.
Current wiring on the backplate is L,N, HW to 3, CH to 4.
Digistat has exactly the same connections but I'm having difficulty getting it to operate correctly - The L & N connections are the same however the manual (and only circuit diagram I can find) shows a switched live to 1 & zone connection to 3.
I obviously don't have a switched live (no stat) & 2 Zones.
The manual does mention linking L & 1 if no separate controller but this just fires the boiler constantly.
I cannot install any additional cables.
So I'm thinking keep the LP722 for hot water & timer for heating, use the timed CH feed for 1 & heating zone 3?
Any help before I go through the tedious process of contacting Drayton tech support would be appreciated.
Thanks
Since getting back into the trade a few years back have installed controllers for boilers with room stats etc & the odd new S plan system - infrequently & admit I am not well versed in heating controls though can follow a circuit diagram!
Customer has asked me to install a Drayton digistat RF3 to his current set up on a Vaillant ECOTEC plus boiler feeding an S plan heating & water. This system is currently ran from a Drayton LP722 dual channel controller & has never had a room stat connected - purely on/off via controller.
Current wiring on the backplate is L,N, HW to 3, CH to 4.
Digistat has exactly the same connections but I'm having difficulty getting it to operate correctly - The L & N connections are the same however the manual (and only circuit diagram I can find) shows a switched live to 1 & zone connection to 3.
I obviously don't have a switched live (no stat) & 2 Zones.
The manual does mention linking L & 1 if no separate controller but this just fires the boiler constantly.
I cannot install any additional cables.
So I'm thinking keep the LP722 for hot water & timer for heating, use the timed CH feed for 1 & heating zone 3?
Any help before I go through the tedious process of contacting Drayton tech support would be appreciated.
Thanks