I have installed a 16a 3 phase extract fan, when doing my testing after id finished i had 403v between phases, boss thinks this is ok but i think its a bit low, anyone?
 
If it's consistently between all phases then as Lenny says it's fine. If for some reason you were getting a wide variance between two of the phases it would be a cause for more head scratching.
 
What is the voltage at the origin of the installation? from this you can determine the voltage drop and wether it is acceptable or not i.e. does it exceed 5%.
it would need to be 424 V at the origin or more to exceed 5% on the voltage you have given. Another deciding factor is what the manufacturers instructions say is the minimum limit.
 

Reply to Drop over 3 phases in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
818
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
884

Similar threads

  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
765
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top